Discuss Hive Help - Hive with Potterton Promax 12 SL boiler in the Central Heating Systems area at ElectriciansForums.net

Connect terminal 3 to 9. From what I can see/make out terminal 1&2 perm live, terminal 3&4 neutral, 6 switch live to boiler and pump, 7 HW on from programmer which is connected to common of the cylinder thermostat, 8 normally closed from cylinder thermostat and 9 is switch live from old room thermostat to brown of the ch valve. If you connect 3 on hive to connector block 9 in wiring centre job should be a goodun :)
 
I'll try in morning mate, but how come old wiring was connected to terminal7 as in the picture. Terminal7 will only have one wire if I take #3 out and put it in 9
 
ps there's no separate thermostats for heating, it was built in to programmer
That confirms my thinking mate as the old programmable room thermostat would have had live connected to the permanent live either terminal 1 or 2 and the switch live from programmable room thermostat would be connected to terminal 9 which switches the brown of the CH valve.
 
So after my missus kicking me at 6:30 in a house that was 14 degrees saying "sort that bloody heating out!" I gave it another look. And one saying comes to mind - "I can't see the wood for the trees".

And it was definitely a forest in the wiring centre. Basically I was wiring the #3 terminal of Hive to #7 in the wiring centre. Why? Because I swear that's where the old programmer switch return went to. But on looking again today, Lee, you were absolutely spot on. I'd traced the wires wrong in the 'jungle centre' and had instead removed the black which wasn't the programmer return, but what I can only assume runs off to the boiler somewhere. Anyway, replaced the 'wrong' black, and actually removed the right black from #9 and then put in my new black from Hive #3 and we have heat.

I've since drawn out the wiring centre to paper and if I get time today I'm going to go through it to learn what goes where, but Lee, I owe you a pint mate.
 

Reply to Hive Help - Hive with Potterton Promax 12 SL boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
596
Picture taken from another post as my phone is a potato. We have had a Potterton Promax Ultra 24 ErP Combi installed. I am looking to install a...
Replies
7
Views
2K
hi need help with wiring this. basically new build with combi boiler, unvented cylinder with dual channel hive ive attached pics with the wiring...
Replies
39
Views
6K
Hello, I'm in the process of changing my wired remeha thermostat with the wireless hive mini, I've had a look at the manual and believe I have...
Replies
5
Views
3K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
458

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock