K

Keith51

My first post so I hope I get this right!
i have just fitted a Honeywell Accenta mini gen4 with lcd remote keypad for my dad. All seemed to go fine until I tested the system. The initial power up was as the manual suggests and the LCD keypad read "system unset". I then entered P and the engineer's code 9999 and the keypad read 0>walk test, again as the manual said. However, on pressing 0 to activate the walk test the keypad started a continuous beeping although the readout was as the manual said. I performed the walk test and the numbers changed from 0 to 1 as they should but no noise as they activated other than the continuos beeping. This happened when I checked the strobe and siren - they work as they should but the beeping sounded as before. I decided to try to arm the system and again all that happened was a continual beeping sound which lasted for 2 to 3 minutes before I reset the system with the default code - the system wouldn't arm.
i have rechecked the wiring and even removed the 4 PIR wiring leaving only the exit contacts wired and still the same happens. I am at a real loss - any suggestions would be really great. Thanks
 
Sounds like you have a tamper fault, either the control panel, or bell box covers are loose. First job replace all factory links and test control panel fully. Then continue, one zone at a time.
 
9 times out of 10, back tamper on bell box not making with wall surface. check for 12V across + and T.
 
Last edited:
Can't get down to my dad's until Thursday when I will try all the suggestions - thank you. However, the manual doesn't say to disable the unused zones but I'll try anything.
 

Reply to HONEYWELL ACCENTA MINI 8SP399A Remote keypad problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, could do with some help please. I installed a Accenta G4 Mini alarm system with x3 LED keypads about 4 years ago which has been working fine...
Replies
1
Views
2K
I have an accenta G4 system which haven't used for a couple of years and the bell box only sounds for a few seconds once activated then turns off...
Replies
3
Views
3K
Hi all, just powered up a G4 Accenta and I'm having trouble with the remote keypad. The red and green indicator led's are lighting up,but thats...
Replies
8
Views
2K
Just replaced one of 2 RKPs within Accenta 6 system with ADE Gen4 keypad without trouble. Both lights are on, all buttons produce a beep and the...
Replies
13
Views
5K
Hi all, just powered up a G4 Accenta and I'm having trouble with the remote keypad. The red and green indicator led's are lighting up,but thats...
Replies
9
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock