Hi! I will be installing honeywell accenta mini alarm soon for the first time. Everything seems to be easy according to the installation manual. The only thing that concerns me is that I've put 6 core cable for 3 PIR and 2 door contacts to the main panel and in manual it showes that PIR have to be connected between one another on tamper circuit. Does it mean that I have to connect between all 3 PIR as well? It cant be true. Please help. thanks
 
you wire the alarm pair of each PIR into individual zones. then the tampers are all wired in series to form a single tamper loop. known as a global tamper. this is because the cheaper panels are designed that waqy. not a separate tamper circiut for each zone.
 
As tel says. If you use say yellow and green as your tamper wires. Just put yellow(pir1) in panel tamper, then green(pir1) to pir2 yellow, pir2 green to pir3 yellow etc until you have a green left to put in panel. The tamper switches in the pir etc make a series circuit.
 

Reply to honeywell accenta mini wiring of PIRs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
533
Hi, Im an electrician but have been installing the odd alarms for some of my customers too. Used to use the Honeywell Accenta G4 with the...
Replies
2
Views
3K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
212
Hi all, I currently have a Pyronix Enforcer V10 Wireless alarm system. I have some shock/contacts on windows, doors, PIRs, and an external siren...
Replies
0
Views
763
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock