Discuss House supplied via out building in the UK Electrical Forum area at ElectriciansForums.net

D

darren

I'm working on a property with a tncs supply which has the dno cut out in an outbuilding about 20 metres away from the house. They have had a boiler installed in said outbuilding which is connected from the main house via some swa for electrical controls and insulated pvc pipe for the water.House is supplied from 100A enclosed main switch in outbuilding has dual rcd board and the tncs earth has been exported to house.Now the outbuilding also has sockets and lighting installed which are not rcd protected.Do i need to put the ccts in the outbuilding on an rcd? Is it ok to export the tncs in this way?
 
This should be good :)

To extend or export................... only from outbuilding to house this time instead of other way round lol.

BIG bag of popcorn already ordered:wink_smile:
 
What do you mean by exporting the tncs? The consumer side of a tncs is a regular seperate L N and E. The E and N 'combine' (hence the C in tncs) within the DNO head. Could you clarify pls.
12am sockets should be on Rcd if used by unskilled persons. Wiring should be on Rcd if concealed within walls. If its surface, the wiring doesn't need to be Rcd protected.
 
What do you mean by exporting the tncs? The consumer side of a tncs is a regular seperate L N and E. The E and N 'combine' (hence the C in tncs) within the DNO head. Could you clarify pls.
12am sockets should be on Rcd if used by unskilled persons. Wiring should be on Rcd if concealed within walls. If its surface, the wiring doesn't need to be Rcd protected.


What are these when their at home?
 
I'm working on a property with a tncs supply which has the dno cut out in an outbuilding about 20 metres away from the house. They have had a boiler installed in said outbuilding which is connected from the main house via some swa for electrical controls and insulated pvc pipe for the water.House is supplied from 100A enclosed main switch in outbuilding has dual rcd board and the tncs earth has been exported to house.Now the outbuilding also has sockets and lighting installed which are not rcd protected.Do i need to put the ccts in the outbuilding on an rcd?Sockets yes,lights depend on installation methods. Is it ok to export the tncs in this way?Yes.
Extraneous conductive parts in both buildings must be bonded back to the MET in a minimum of 10mm as they are effectively part of the same installation.As long as the distribution circuit over to the house meets the requirements,or a separate bonding conductor is installed the TNCS earth can be used.

...........................
 
Cheers the the useful input wp Perhaps i should have worded my question regarding rcd protection in the outbuilding a little differently. attempt 2:The customer is a tight --- and does not want to pay for a new db for the existing electrical installation in the outbuilding. Even though the house part of the installation meets 17th ed regs the outbuilding does not so do i need to ensure that supplementary equipotential bonding is in place in the house. Cheers
 
you've not said what work you are doing. it's only your work that needs to comply with 17th. also what type of DB supplies the outbuilding sockets etc. fuses or MCBs?
 
Cheers the the useful input wp Perhaps i should have worded my question regarding rcd protection in the outbuilding a little differently. attempt 2:The customer is a tight --- and does not want to pay for a new db for the existing electrical installation in the outbuilding. Even though the house part of the installation meets 17th ed regs the outbuilding does not so do i need to ensure that supplementary equipotential bonding is in place in the house. Cheers

Sorry Darren,I'm a little cofused. You've gone from a query about RCD's in the outbuilding to supplementary bonding in the house. Can you explain the extent of the work you are doing as Tel has asked and it may be clearer.
 

Reply to House supplied via out building in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
562
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
762
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock