Yes. I've taken out a supplier fuse when an entire installation was reverse polarity, and certainly mistakes were made leading up to this, but I learned from it.
I get that you left things working one evening, and the next morning for no apparent reason everything was dead.
Red flag number 1 was obviously that supplier fuse had blown. That would immediately make me think something very significant has happened.
Red flag number 2 was that the RCD and MCB were still in the ON position. So the cause must be upstream of them. This would put me in "something exceptionally unique and wacky has happened" mode and caution levels would rise to paranoid levels.

The absolute last thing I'd do is bung another fuse straight in and 'see what happened'. Continuity/IR testing at your incomer on your CU would be where my mind when next.
As for creating your own low value fuse, still without having any idea what caused the fault or finding a way to measure it, well I'm honestly rather stunned.

Out of interest, what was causing the short, the end of the tails, or the terminal itself?
Was the cut-out safe for continued use afterwards?
Yes there was a red flag moment but think about it, it worked fine, its probably worked fine since the 50's, yes the house had had a fire but it didn't get to the mains cupboard, the old plastic CU was still intact. So what could cause a 80A fuse to blow in the middle of the night with no-one around and absolutely no load on it, its not like the cut out has moving parts that had failed.

My conclusion to the red flag moment was it has to be a faulty fuse, so I replaced it. As for the very thin fuse wire trial, I thought that was quite a good idea, couldn't have been more than an amps worth of wire, I disconnected everything, even the tail out of the top of the fuse holder and it still went with a bang but with a lot less sparks and arcing this time.

s for the problem, I have no idea, I still cant fathom what went wrong, I got the office to call the DNO out and I wrote on the cut out "do not energise" By the time I came back to second fix it had a brand new head on it.


I still don't get all the hoo-ha about it though, it seems some people are ---- scarred of a big bang, you see it when someone is going to cut a cable which might be live with insulated snips, try as they might, they just can't bring themselves to do it even though they know they are perfectly safe from injury, its the bang you see.
 
I still don't get all the hoo-ha about it though, it seems some people are ---- scarred of a big bang
You might want to look up arc-flash injuries. Actually, you don't.

The stats I remember from the USA was that about 80% of deaths suffered by electricians were due to burns, not shock. Now the situation UK versus USA is not quite identical as the USA has more issues of arc-flash for various reasons, but if you have seen what a high energy fault can do on a test rig, etc, you REALLY do not want to be part of it.
 
If you make a big bang like that in full earshot of plumbers, joiners, builders… you’ll either

A- get the p ss ripped out for months on end
B- no one wants you back on a job because even they think it was dangerous.
 
I am not sure that you realise the damage that closing a fuse on to a fault can cause.
on this occasion it seems like you were lucky.
these things can end in loss of life, if your lucky it’s just loss of face (sometimes literal)
my first thoughts are that you are an idiot, after further thought I think you are more educated than the average idiot however have little concern about the effects of your actions and are therefore just a risk taker.
good thing you have found employment because if you start telling prospective employers about your antics they might turn you down.
 
I am not sure that you realise the damage that closing a fuse on to a fault can cause.
on this occasion it seems like you were lucky.
these things can end in loss of life, if your lucky it’s just loss of face (sometimes literal)
my first thoughts are that you are an idiot, after further thought I think you are more educated than the average idiot however have little concern about the effects of your actions and are therefore just a risk taker.
good thing you have found employment because if you start telling prospective employers about your antics they might turn you down.
I really do think most people have never worked on smaller informal sites that don't have the hi-viz brigade looking after them. You wouldn't believe what goes on regarding safety or lack of it. The labourer fell though some joists the other day right up to his -------s and brought a ceiling down with him, did anyone get upset? of course not.

I must live in a different universe to most people, just the other day (admittedly working at home) me and a mate got my RSJ steel into position by lifting it up a block at a time from either end until it was about two meters high, wobbled all over the show but it saved £100 on a genie, it wasn't even me that wanted to do it that way but I got called soft for not just getting on with it.
 
Sound is not quite in sync (earlier than video) due to video compression delay artefacts on cheap dashcam, but here is an illustration of why you wear PPE if working on live power circuits:

I was looking for that video earlier, but couldn't find it.
There's another one where there is no way the person standing where the fireball happened survived, and it's simply too horrific to share a link to.

I really do think most people have never worked on smaller informal sites that don't have the hi-viz brigade looking after them.
This is the last place you want to generalise, we have forum members doing just about everything possible! I'm a sole trader and rarely do site work.
So what could cause a 80A fuse to blow in the middle of the night with no-one around and absolutely no load on it, its not like the cut out has moving parts that had failed.
So far my best wild guess is that things got marginally disturbed when the temporary supply was hooked up, and some kind of significant vibration occurred causing a further minor shift in either the terminal or the tails and BANG.

The bottom line is that a closing on a dead short or even a moderate load load holding an 80A fuse in your hand to complete the circuit is just damned dangerous, and the extent you are arguing against this basic fact leads me to believe you have no intention of ever taking it on board. I don't have anything further to add so won't be debating this any further.
 
I think in this case, the guy needs more experience, which i think he will get soon enough. He never did answer the question of what size fuse would he baulk at energising without IR testing first, still, cannot fault the attitude, like the guy jumping out of a 30 storey building...... so far so good, lol
 
I think in this case, the guy needs more experience, which i think he will get soon enough. He never did answer the question of what size fuse would he baulk at energising without IR testing first, still, cannot fault the attitude, like the guy jumping out of a 30 storey building...... so far so good, lol
More experience, I'm 52 and have had more than most.

Its no good asking this question, how can you test a cut out before you put the fuse back in, I'll pull plenty of fuses out over the next months and years an I'll put plenty back in again, I'm not about to do a full forensic on every little thing I do from now on on the off chance that a 0.00001% fault will occur. I'd rather take my chances.
 
I was looking for that video earlier, but couldn't find it.
There's another one where there is no way the person standing where the fireball happened survived, and it's simply too horrific to share a link to.


This is the last place you want to generalise, we have forum members doing just about everything possible! I'm a sole trader and rarely do site work.

So far my best wild guess is that things got marginally disturbed when the temporary supply was hooked up, and some kind of significant vibration occurred causing a further minor shift in either the terminal or the tails and BANG.

The bottom line is that a closing on a dead short or even a moderate load load holding an 80A fuse in your hand to complete the circuit is just damned dangerous, and the extent you are arguing against this basic fact leads me to believe you have no intention of ever taking it on board. I don't have anything further to add so won't be debating this any further.
With the greatest respect I won't be taking it onboard, I just dont see how you can guard against this, it was one of those "---- happens" moments and will more than likely never happen again in my lifetime.
 

Reply to How easy is it to blow the DNO's cutout? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock