as a starter, i tend to plan downlights at 3ft apart. this distance gives a decent illumination and gets the fittings bang central between the joists ( assuming 18" spacing ).
 
and too the modern man, dont go over a 1000mm between lights and 500mm off walls, i did a rare shaped room last week and it ended up every 850mm one way and 900 another to miss any joists.

and if too bright fit 35w bulbs/lamps or leds

i also found dimming leds isnt that good
 
and too the modern man, dont go over a 1000mm between lights and 500mm off walls, i did a rare shaped room last week and it ended up every 850mm one way and 900 another to miss any joists.

and if too bright fit 35w bulbs/lamps or leds

i also found dimming leds isnt that good

Weird how different people work, always cool too see how differnent sparks work. I wouldn't go further than 1500 between lights and 750 off walls. In a kitchen I tend to go 600 off the wall (Unless a tallboy, try to go 750) Ideally I like them at 120 apart
 
I usually go 1m in on lounge's and bedrooms but go for about 700mm in kitchens and spread them no more than a meter and no less than 800 really
 
I find kitchens tricky due to the number of wall units that can "appear" after the lighting is done. Stick a nice IP rated florry up. No flies get in, and a nice spread of light :)
 
I find kitchens tricky due to the number of wall units that can "appear" after the lighting is done. Stick a nice IP rated florry up. No flies get in, and a nice spread of light :)

Must admit that I'd not thought of IP rated fittings just to keep flies out. OK if the customer is into the industrial look!
 
My builder mate is planning to fit 20 in his kitchen / diner.

Last time I saw something like this was in a film with Johnny Mills in it, he was trying shoot down so Fockkers flown by the Luftwaffer over Blighty.

He was also sorting Sylvia Syms out at the time as well as saving us all from the cruel hun......and poor Caruthers took a packet over the channel ..............

And I bet his bank of 60 inch Carbons did not give off as much light as those
 

Reply to How many LED downlights for my kitchen? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I am currently in the process of building an extension and I need to purchase some led downlights for my kitchen but unsure how many I...
Replies
4
Views
306
Looking through the fire-rated downlights out there on the market, Integral Evofire claims its canless design would let the heat off and hence...
Replies
8
Views
211
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
316
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
224
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock