Discuss How many total amps is this?? in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
My 50 amp breaker at the bottom just tripped I’m trying to figure out why. Is there too many amps being pulled in the house? I don’t use that top Left 50 amp breaker.

the 50 amp is wired with 6/2 wire to a sub panel that pulls 8000 watts. It’s definitely oversized. The project called for 40 amps but I upgraded just to be safe.
 

Attachments

  • 48710AEA-8D2A-4D4A-99F8-B1B44297239C.jpeg
    136.8 KB · Views: 21
Last edited:
Hi from UK and I hope you are keeping well :) .
Pardon my basic question, but is the 8kW load run from a 120V circuit? 8kW at 120V would be 66A and that would likely trip a 50A after some time.
 
Hi from UK and I hope you are keeping well :) .
Pardon my basic question, but is the 8kW load run from a 120V circuit? 8kW at 120V would be 66A and that would likely trip a 50A after some time.
No it is on a double pole.

so let me go into more detail. The 50 amps is running into what is called a Titan Control 8x light controller. It works similarly to what a sub panel would. That Titan controller is connected to 8 ballasts each powering 1000 watt horticulture lighting bulbs totalling to a max of 8000 watts. The controller has two separate 120v cords that are plugged into a wall timer so if you wanted to turn on 4 lights at this time and another 4 at a different time, you could. The timer will tell when the power is to be shut off and turned on by controlling a magnet inside the Titan controller. It’s been working fine the past 2 weeks as this is a fairly new setup I have built. Prior to this incident the one thing I did differently was I adjusted both timers to basically turn on at the exact same time almost down to the second. Before there was an offset of about 1 minute. When the ballast first turns on it takes a considerable amount of energy. So I am assuming this was my mistake. Maybe causing a surge of some sort

another one I would like to point out is that I wired the whole damn thing wrong but apparently it turned out to be okay? I’m not sure so let me hear your take on this. I wired the double pole as normal hot and hot. But I put the ground into the neutral bus. I think that could be the reason also. So I researched online and some were saying it was okay to wire neutrals and grounds together if some requirements were met.

When the breaker tripped I flipped it back to the on position it immediately tripped again shutting off my entire house electric supply and frying my 50 amp breaker. I had to go outside to turn the power back on.. I know I know. I made a bunch of mistakes. But all is well and no fire so that’s a plus. Good thing it was raining a lot today ?

any ideas what happened here?
 
Hi - it’s always possible there’s a wiring fault, oops !
But if it was working ok till you changed the light timing to all come on at once then the inrush current you mentioned may well be the cause. Of the first trip.

I never connect Ground and Neutral, so I’m wondering why that’s been done? This would likely trip a ground fault device for example.
 

Reply to How many total amps is this?? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
649
I have a sub panel about 75ft from my house attached to my shed that feeds a pool pump, some outlets and a pool heater which is no longer used...
Replies
0
Views
547
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
736
Trying to connect a 50 amp inlet box to my Siemens outdoor combination panel 200 amp cutoffs. Can’t figure out where to insert the 50 amp breaker...
Replies
1
Views
855
Trying to connect a 50 amp inlet box to my Siemens outdoor combination panel 200 amp cutoffs. Can’t figure out where to insert the 50 amp breaker...
Replies
0
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock