It depends on what it is you want the motor to do.
If the output torque when wired in star is sufficient for the job you want the motor to do, then it can be wired in star.
If it is insufficient, then it will have to be wired in delta.
If the output torque required is so great, that the start up current will cause an overcurrent, then you will have to use a star/delta starter.
This allows the motor to be started in star, and when the motor is running at ideally 75-80% of the delta speed, contactors change the wiring configuration from star to delta.
 
Check the rating plate. It will give the voltage and connections, some will give two voltages.
400V Star
220V Delta

If it shows 400V Delta them it is suitable for star / delta starting.

It is inefficient to run a 400V delta motor in star
 
Thermal or electronic set at 100%
Dash pot 115 to 125% but you have to know how to set the time lag.
 
Last edited by a moderator:
Yes, get in to the old heavy stuff and it’s still there. It’s like me and you, old but works when needed.

It’s one thing I’m dreading in starting the “Motor” sticky in this forum. I’ve got to get my brain back in gear
 
As with everything within industrial electrics, wire as per manuf. instructions. In this instance the motor plate tells you almost everything you need to know. You need to know what supply characteristics you're applying to the motor you have. If you have a 3 phase 400Vac supply and a DOL starter then the plate tells you to connect it with respect to the ratings.
MotorPlate.jpg
 
also come across 400/660V or maybe 415/690V or something similar a few times (the most recent 2 week ago), you wanna connect that as per Delta when using a 400V supply.
 
12-18 months ago I carried out a maintenance check on a bottle inspection machine and declared a motor, in a wet area, needed monitoring due to low(ish) IR reading. This is the original's plate.

SDC106872.jpg


It caused a little confusion. The hierarchy decided to get in a 3000rpm 50hz model and have it fitted to allow the original to go for overhaul. The machine would not run correctly due to obvious speed differences!
 
Last edited by a moderator:

Reply to How to know whether to wire as star or delta? in the Canada area at ElectriciansForums.net

Similar Threads

Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
973
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock