Hi,

I am looking to get an electrician to upgrade my consumer unit and do some work on circuits. At the same time, have been receiving letters from E-On about upgrading to smart meters - this was supposed to happen a few years ago but when they visited, they refused to carry out any work.

Looking around the Internet, I can't find any images that represent the service head that I have installed at my house. My understanding is that this is really old and needs upgrading ASAP (images attached)

So a few questions I have:
  • As the DNO owns the Service Head - how do I go about asking them to upgrade it (for free!), what do I say? I've sent them an email on Monday asking for inspection and awaiting a response
  • If you look at the picture, the earth that is clamped to the board - is it supposed to be black? Look a bit burnt or could it be this black dripping thing I've read about?
  • How long would it take to upgrade this?
  • Can an electrician replace the consumer unit with this setup (i.e. the service head not upgraded)
  • What fuse would I likely have?
  • Are there any other concerns I should be aware of? (just by looking at this)

Any help would be very appreciated.
Many thanks.
 

Attachments

  • photo_2021-10-26_22-17-59.jpg
    63.8 KB · Views: 153
  • photo_2021-10-26_22-17-54.jpg
    68.6 KB · Views: 142
Hi,

I am looking to get an electrician to upgrade my consumer unit and do some work on circuits. At the same time, have been receiving letters from E-On about upgrading to smart meters - this was supposed to happen a few years ago but when they visited, they refused to carry out any work.

Looking around the Internet, I can't find any images that represent the service head that I have installed at my house. My understanding is that this is really old and needs upgrading ASAP (images attached)

So a few questions I have:
  • As the DNO owns the Service Head - how do I go about asking them to upgrade it (for free!), what do I say? I've sent them an email on Monday asking for inspection and awaiting a response
  • If you look at the picture, the earth that is clamped to the board - is it supposed to be black? Look a bit burnt or could it be this black dripping thing I've read about?
  • How long would it take to upgrade this?
  • Can an electrician replace the consumer unit with this setup (i.e. the service head not upgraded)
  • What fuse would I likely have?
  • Are there any other concerns I should be aware of? (just by looking at this)

Any help would be very appreciated.
Many thanks.
As the dno...
Highlight the fuse in the neutral - see below.
Depending on the amount of compound leakage - may be worth mentioning.

If you look at the picture...
The normal colour for this wire should be yellow/green, if older it could be just a green colour, and yes very old could have been black, however this would be unusual as it was normal to be completely bare. The black you are seeing is the tar type compound used as insulation in the service head, there is often minor leaking which isn't a problem, however if extensive then it is an issue.

How long would it take...
The dno would only take a couple of hours or so.

Can an electrician...
Yes, but they will highlight the issue of two fuses (see below) and it is probably best to get the service head done first.

What fuse...
They could be a wide range of values between 30 and 60A (often 40A) in that era, but actually could be up to 100A if they have been updated. HOWEVER the main issue is that there appears to be a fuse in both line and neutral - very common originally, however this is unacceptable practice today and should be addressed.

Are there any...
The fuse in the neutral is the most concerning - highlight this to the dno.

The earth wire is actually very undersized for modern practice, but will be addressed by changing the service head.

When you get a new consumer unit etc the electrician will use this larger cable, if this smaller cable is all that is there then there may be a big issue with fault levels and loop impedance (Ze and Zs) at various places in the installation, which needs to be confirmed by the electrician before he can energise. Hence probably better to get the head replaced first.
 
Just by looking at that service head i would say that an EICR should be carried out before changing the CU.........A good bet the place needs rewiring
This is what I was thinking at first, but in a kitchen refit earlier this year, I was able to see the cables running between the floor/ceiling. T+E are 2.5mm^2 solid copper, some in white PVC others in grey but obviously with the old wiring colours.

There are some tin-copper wires which are either cut or no longer connected to anything left behind.

And, looking at the meter board, I think the space there, I assume was a previous fuse box or the like. On the CU, it has a "100A Main Switch".

So I think it was rewired once at some point.
 
As the dno...
Highlight the fuse in the neutral - see below.
Depending on the amount of compound leakage - may be worth mentioning.

If you look at the picture...
The normal colour for this wire should be yellow/green, if older it could be just a green colour, and yes very old could have been black, however this would be unusual as it was normal to be completely bare. The black you are seeing is the tar type compound used as insulation in the service head, there is often minor leaking which isn't a problem, however if extensive then it is an issue.

How long would it take...
The dno would only take a couple of hours or so.

Can an electrician...
Yes, but they will highlight the issue of two fuses (see below) and it is probably best to get the service head done first.

What fuse...
They could be a wide range of values between 30 and 60A (often 40A) in that era, but actually could be up to 100A if they have been updated. HOWEVER the main issue is that there appears to be a fuse in both line and neutral - very common originally, however this is unacceptable practice today and should be addressed.

Are there any...
The fuse in the neutral is the most concerning - highlight this to the dno.

The earth wire is actually very undersized for modern practice, but will be addressed by changing the service head.

When you get a new consumer unit etc the electrician will use this larger cable, if this smaller cable is all that is there then there may be a big issue with fault levels and loop impedance (Ze and Zs) at various places in the installation, which needs to be confirmed by the electrician before he can energise. Hence probably better to get the head replaced first.
Thank you for answering and highlighting the fused neutral - I've done some research and see the importance of replacing this ASAP.

I've contacted UKPN twice and on both occasions, they've said that I have no authority in reporting this or making such requests - they can only speak to the supplier about reports of the cut-out

First call
I asked for the replacement of the fused neutral cut-out and referred to the earthing - they replied why? I said I want to upgrade to a smart meter and they said I need to contact my supplier and if they can't install it for any reason, they need to report to the DNO.

Second Call
I asked for a home visit: they found information from the previous supplier visit (when they refused to install a smart meter). This is a code C that doesn't require attention, it simply means 'information only'. They then told me to contact the supplier to get them to upgrade this code C to code A or code B if the cut-out needs replacing. They echoed the same as my first call, they don't respond to requests from consumers. I've contacted their Customer Care to get a copy of this information in writing.
 
You could highlight to them that the service head appears dangerous with a fused neutral, and that it therefore breaches ESQCR 2002 regulations Part VII Regulation 24 paragraph 1 (a,b&c) which puts the responsibility squarely on the shoulders of the DNO as follows:


24.—(1) A distributor or meter operator shall ensure that each item of his equipment which is on a consumer’s premises but which is not under the control of the consumer (whether forming part of the consumer’s installation or not) is—

(a)suitable for its purpose;

(b)installed and, so far as is reasonably practicable, maintained so as to prevent danger; and

(c)protected by a suitable fusible cut-out or circuit breaker which is situated as close as is reasonably practicable to the supply terminals.

As having a fused neutral and potentially single insulated (old) conductors it fails on all three points

A) It is not suitable (fused neutral)
B) not been maintained in line with regulations
C)the fuse is not suitable , being in the neutral.

All dnos were supposed to ensure all fuses in the neutral were removed by 2013 as The ESQCR state that, as of 31st January 2013, fused neutrals shall not be retained. There is an HSE requirement for fused neutrals cut-outs to be removed within 28 days of being identified.

The Electricity Safety, Quality and Continuity Regulations 2002 also state under section 2 (iii) Pre-1937 cut-outs with fuses in earth or neutral conductors must be removed from service by 2013.
 
if there is a fuse in the neutral, not a solid link,then DNO are obliged to attend and rectify. nothing to do with supplier.geton the phone and insist on a visit. theaten to contact ofgen.
 
You could highlight to them that the service head appears dangerous with a fused neutral, and that it therefore breaches ESQCR 2002 regulations Part VII Regulation 24 paragraph 1 (a,b&c) which puts the responsibility squarely on the shoulders of the DNO as follows:


24.—(1) A distributor or meter operator shall ensure that each item of his equipment which is on a consumer’s premises but which is not under the control of the consumer (whether forming part of the consumer’s installation or not) is—

(a)suitable for its purpose;

(b)installed and, so far as is reasonably practicable, maintained so as to prevent danger; and

(c)protected by a suitable fusible cut-out or circuit breaker which is situated as close as is reasonably practicable to the supply terminals.

As having a fused neutral and potentially single insulated (old) conductors it fails on all three points

A) It is not suitable (fused neutral)
B) not been maintained in line with regulations
C)the fuse is not suitable , being in the neutral.

All dnos were supposed to ensure all fuses in the neutral were removed by 2013 as The ESQCR state that, as of 31st January 2013, fused neutrals shall not be retained. There is an HSE requirement for fused neutrals cut-outs to be removed within 28 days of being identified.

The Electricity Safety, Quality and Continuity Regulations 2002 also state under section 2 (iii) Pre-1937 cut-outs with fuses in earth or neutral conductors must be removed from service by 2013.
I've contacted UKPN emergencies department and they've also said I need to contact the supplier regarding the fused neutral. They require a B11 flow from the supplier.
But, for the black earth wire, they will be sending someone out to have a look soon.

I contacted E-On and the earliest appointment they've given me is 10th December - this is to attempt to install a smart meter which I assume they cannot and result in them reporting the situation to UKPN.
 
I've contacted UKPN emergencies department and they've also said I need to contact the supplier regarding the fused neutral. They require a B11 flow from the supplier.
But, for the black earth wire, they will be sending someone out to have a look soon.

I contacted E-On and the earliest appointment they've given me is 10th December - this is to attempt to install a smart meter which I assume they cannot and result in them reporting the situation to UKPN.

Nothing's ever easy!
 

Reply to How to upgrade really old Service Head, Meter and Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
848
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
789
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
606
Hi guys, I'm shadowing the electrician who is doing our EICR's and after visually inspecting the service cable and service head, I noticed a bit...
Replies
12
Views
1K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock