Discuss Hypothetical EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

diditrain

-
Arms
Reaction score
182
If you were asked to carry out an EICR on an socket outlet circuit installed post 2008, not directly intended for outdoor use, but not given any form of RCD protection, then what code could/would you attribute to this situation?

Domestic situation
 
That's actually a good question. The thing you would have to find out is the date of the installation design. If it was designed to the 16th edition it would be a code 3 regardless of the installation date.
 
it's a question of risk. it's not the socket outlet per se that may pose a potential hazard. it' s what is plugged in and the use. if it's for stationary equipment like PCs, TVs etc., i'd code it as a C3. if the use of equipment that poses a risk, then a code C2 would be appropriate.
 
I would tend to feel that if it were designed to the 17th then it is non compliant with the regulations in force at the time, however you are assessing the installation for safety for continued use as it stands now so the date of install is immaterial. If the socket is not presenting a danger but the risk level is higher than it would be if it were installed correctly today then there is room for improvement so a C3.

If it were installed in 2013 or 1913 the situation is the same, is it safe?
 
Personally, I don't think that you can see a problem, make an assessment and then claim it's more or less dangerous depending on how long it's been there for - a bare wire is a bare wire regardless of whether it's been like it for 50 years or 50 minutes. So, I think I'd be looking at a C3 on that regardless of date.
 
You can't go round issueing C2's for sockets without RCD protection unless its outside and then I'm wary of even doing that!
 

Reply to Hypothetical EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
406
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825
Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock