Discuss If you can't split a circuit? in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
0
I am a retired electrician and I've been out of the game for a while. My son asked me a question the other day and I wasn't too sure how to answer it so thought you lot might.

He wants to use rails to supply 5 modules, each module will have 40 small actuators that operate at 24VDC at 0.9As. Normally I said he would split each module up into a separate circuit with each one on an RCBO but as they are all attached to the one rail he can't do that. Is the only option to have a huge RCBO?

Interested in what innovative ideas you can come up with?
 
That is totalling about 5kW so not a trivial load, though possibly less on average depending on the usage. So you might be OK with a 25A C-curve RCBO, but:
  • What does the Manufacturer's Instructions say about supply side protection?
  • Do they need RCD protection, or is MCB sufficient? (i.e. is it hard wired and low risk of shock, or in area where additional protection is needed)
  • If they need RCD protection, what sort of total leakage current will the whole thing have? (back to the MI spec again)
 
A very general comment, without knowing the actual application, but wonder if the control circuitry should be separated from the load circuitry. e.g. one circuit running control gears and relays, and then the actuators powered in groups by individual circuits.

(I'm also intrigued where the 24vdc is coming from, as it may need to be multiple sources)
 
Presumably the (5x) Module is the source of the 24v dc for each (5X) set of 40 actuators?

Is this "One Rail" a Din rail that the Modules are clipped onto, or is it a Bus Bar as a common feed to each Module?

Is all this in a control cabinet?
Is it for commercial or personal use?
 
Have I got this right?
5 modules x 40 actuators x 0.9A = 180A at 24V DC
That's a lot of current. Battery supply?

I would certainly split the system into 5 modules and fuse each, probably at 32A. That's just for basic safety. No excuses as it protects against a screwdriver in the wrong place. A sixth fuse would feed any control circuit, if required.

Normally I wouldn't consider earth leakage protection on a 24V DC system, although it can be done. It's not a cheap option on DC systems.
 

Reply to If you can't split a circuit? in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
847
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi there. I am a doing some DIY kitchen work. In Ontario Canada, code allows either a split 15 amp multi-wire circuit or a 20 amp circuit (each...
Replies
0
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock