Hi there,
I'm Currently doing my design calcs for my college project and doing the actual Zs calculation.
Formula is Zs= Ze (or Zdb) + (R1+R2)
Then for (R1+R2) you find the (R1 +R2) per metre value in the On site guide appendix i - i1 , which for me line and cpc are both 1mm so its 36.20 . I then need to multiply this by the length of the circuit which is 30m and multiply by the factor for maximum operating temperature then divide this by 1000 to convert to ohms . And in the table i3 it gives u 2 options of conductor installation: Not incorporated with cable and not bunched or Incorporated in a cable or bunched. And I'm using 1mm single core cables for this circuit which will be installed in the same conduit together so I'm pretty sure that this would be classed as bunched but I wanted to double check.
 
Read up on the definitions of conductors, then circuits. Then double check what bunching is defined as - and the answer will be apparent PLUS you’ll probably end up learning something else as well along the way. Oh…… and well done on fully stepping through your maths!
 

Reply to If you have 3 single core cables in conduit for a singular circuit would this be classed as bunched? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
896
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock