- Reaction score
- 7
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure.
Zsc= Zesc(or Zdbsc) + (R1+RN)
(R1+RN) = milli ohms/metre x length x correction factor and then divide that by 1000
Zesc = Uo divided by PFC
Then add together Zesc and (R1+RN)
Then Isc = Uo divided by Zsc
But the fact that my formula says Isc (short circuit current) at the end and not PSCC makes me thing it could be a slightly different formula and i dont want to do all the work to be told its the wrong formula
Ive done one circuit so far so i will give an example
Single core 1mm cables
(R1+RN) = 36.20 x 29.25m x 1.04 =1101.204 and then divide this by 1000 gives me 1.101204 ohms
PFC is 3.7kA or 3700A
Zdbsc = 230v divided by 3700A which = 0.0621
soZsc = Zdbsc + (R1+R2) = 1.101204 + 0.0621 = 1.163304 and this to 2 decimal places is 1.16 ohms
Isc = Uo divided by Zsc which = 230v divided by 1.16 ohms which = 198.27586... and this to 2 decimal places = 198.28A
And 198.28A is 0.19828kA and that to 2 decimal places is 0.20kA
0.20kA is my final answer but is that just the short circuit current and if so is that the same as the prospective short circuit current or have I indeed got the wrong formula
Zsc= Zesc(or Zdbsc) + (R1+RN)
(R1+RN) = milli ohms/metre x length x correction factor and then divide that by 1000
Zesc = Uo divided by PFC
Then add together Zesc and (R1+RN)
Then Isc = Uo divided by Zsc
But the fact that my formula says Isc (short circuit current) at the end and not PSCC makes me thing it could be a slightly different formula and i dont want to do all the work to be told its the wrong formula
Ive done one circuit so far so i will give an example
Single core 1mm cables
(R1+RN) = 36.20 x 29.25m x 1.04 =1101.204 and then divide this by 1000 gives me 1.101204 ohms
PFC is 3.7kA or 3700A
Zdbsc = 230v divided by 3700A which = 0.0621
soZsc = Zdbsc + (R1+R2) = 1.101204 + 0.0621 = 1.163304 and this to 2 decimal places is 1.16 ohms
Isc = Uo divided by Zsc which = 230v divided by 1.16 ohms which = 198.27586... and this to 2 decimal places = 198.28A
And 198.28A is 0.19828kA and that to 2 decimal places is 0.20kA
0.20kA is my final answer but is that just the short circuit current and if so is that the same as the prospective short circuit current or have I indeed got the wrong formula