I've been out of this thread for a few months while I followed the Nanode-based control solution that was discussed in earlier posts. I have done the assembly and mimicking and am about to connect to the 5V version of the same controller - MCPC2450A

pmcalli, do you have the output filtered? If so what have you used?

The I/P is filtered to stop fast turn on edge causing interference. I have used a standard emc filter from rs stock number 7024019
 
I have now completed testing of meter behaviour and have very bad news for you. The meter measures true power and your analog multiplier measures apparent power so you will be feeding back uneccesary power. I have now tested using a synchronous demodulator and it correctly follows true power as measured by the meter. The other advantage is the circuit is unchanged whether you use one ct on composite meter tail or two cts on seperate meter tails.

No, the bad news is the other way round. If you are just doing synchronous demodulation of the current waveform you are not using any voltage waveform information (other than the zero-crossing points), so you are assuming that its waveform is the same as the current. This is only true if you have a pure resistive load, which may not be the case.

As suntrap has pointed out already in posting #388, what I am doing is multiplying instantaneous current by instantaneous voltage and then averaging the result over (at least) one cycle.

That this will work with any load or combination of waveforms to give true rms power is a well-known mathematical result, if you are not familiar with it then read this paper

http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.134.5837&rep=rep1&type=pdf

or these articles

Power Measurement Article

Voltage, Current, Power & Energy : Definitions :: Electronic Measurements.
 
Last edited:
No, the bad news is the other way round. If you are just doing synchronous demodulation of the current waveform you are not using any voltage waveform information (other than the zero-crossing points), so you are assuming that its waveform is the same as the current. This is only true if you have a pure resistive load, which may not be the case.

As suntrap has pointed out already in posting #388, what I am doing is multiplying instantaneous current by instantaneous voltage and then averaging the result over (at least) one cycle.

That this will work with any load or combination of waveforms to give true rms power is a well-known mathematical result, if you are not familiar with it then read this paper

http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.134.5837&rep=rep1&type=pdf

or these articles

Power Measurement Article

Voltage, Current, Power & Energy : Definitions :: Electronic Measurements.

Many applogies I didn't read your post properly I mixed you up with another poster who is using an analog devices true rms device fed from current taps which will only deliver apparent power. Thanks for the links best explanation I've seen. However your statement is not 100% correct. If you synchronously demodulate the current waveform with the voltage zero crossings you do get true power. A simple simulation with sine waves out of phase proves this. What happens with non sine waves I havent analysed. I have been running some tests against my meter which is of the spinning disk type and found firstly that the meter reads 4.6% low yip yip hooray but also creeps at 0.1kwhr when the controller is running the immersion at 2 to 3 kW. In my two ct circuit this can be compensated but not in the single ct without applying a higher offset which is not desirable for winter use. The unfortunate conclusion is that if I had been measuring apparent power then this problem would not occur as the current would be over reported. I suspect my meter is responding slightly to apparent power. Can you remind me which analog multiplier you are using and I will try it out as a measuring device to identify the cause of my creep.
 
I found found that to deal with the problem I have had to use two vairiable gain amps wich have allowed me to tune out the problem at the 2 to 3 kw point. I know 0.1 was only a small input but I didn't want to pull anything.
 
I found found that to deal with the problem I have had to use two vairiable gain amps wich have allowed me to tune out the problem at the 2 to 3 kw point. I know 0.1 was only a small input but I didn't want to pull anything.
Any idea to the cause. I have stupidly been concentrating on trying to get true power when apparent power would actually have given some margin to this effect. On my systems I see the effect on both a two ct balanced system and a single ct on composite meter tail. In the 2-3 kW range most of the power is resistive so I can only speculate that either the current taps are non linear or the meter reads the composite waveform incorrectly. I will try the suggested analog multiplier but not hopeful as I have had previous bad experience (over 25 years ago mind ) with this device beacuse of non linearity effects of up to 5%?. I will also try my demodulator circuit with added hysteris in the mains voltage squarer this will give a selectable phase shift and hence give the same effect as miss balancing the two ct circuit which was very successful. I am desperate to get a solution to this as I have a queue of people whoose installer used a spare way in the consumer unit making a two ct design difficult to implement.
 
I too have been battling with ever changing errors on the export rate. I have built and tested many many variations using different coils and approaches. I have noticed when inductive loads kick in ie. Washing machine and the fridge and freezer loads, these change the way the circuit will compare the power loads due to lag or lead on the current angle. It has all come to a compromise. I have now settled on the circuit that gives me adjustment on the buffering op amps. I have been told. Don’t let perfect be the enemy of good! I have been striving for perfection on the’ no export’, but Unless I spend a lot of money and map all this in a plc ( EMMA ) I am not going to get it. I am now happy to settle with ,< 120 watts export generally and up to 250 if the house has a heavy inductive load running. After all the testing and different approaches I am only marginally better than my original design. But hey it’s been fun. I now have to make some up for my friends who are all nagging me. Without this forum it would have been a lot harder.
 
Many applogies I didn't read your post properly I mixed you up with another poster who is using an analog devices true rms device fed from current taps which will only deliver apparent power. Thanks for the links best explanation I've seen. However your statement is not 100% correct. If you synchronously demodulate the current waveform with the voltage zero crossings you do get true power. A simple simulation with sine waves out of phase proves this. What happens with non sine waves I havent analysed.

That's OK, no problem, at least unlike the true rms converter your synchronous demodulation will give the direction of power flow. Perhaps I should have said a linear rather than resistive load, because I agree that this technique will cope with sinusoidal current out of phase with the voltage.

But I still think it will fall down if there is any harmonic current. Another way of thinking of it is that your square demodulation waveform contains odd harmonics (1/3 3f, 1/5 5f etc) which are not actually present in the voltage waveform, so if there is any harmonic current at these frequencies it will give corresponding spurious terms in the expression for power. This is probably addressed in the paper above but I confess I have not actually looked it up.

Can you remind me which analog multiplier you are using and I will try it out as a measuring device to identify the cause of my creep.

I have sent you a PM about this as it is not the device I referred to in my original posting.

The I/P is filtered to stop fast turn on edge causing interference. I have used a standard emc filter from rs stock number 7024019.

Is this effective? I have fitted the even more expensive Schaffner multi-stage filter suggested by others, but there is still a 100Hz buzz from the unit, from the immersion heater itself and on AM radio. So I am now trying out an entirely different approach which may also work out cheaper.
 
That's OK, no problem, at least unlike the true rms converter your synchronous demodulation will give the direction of power flow. Perhaps I should have said a linear rather than resistive load, because I agree that this technique will cope with sinusoidal current out of phase with the voltage.

But I still think it will fall down if there is any harmonic current. Another way of thinking of it is that your square demodulation waveform contains odd harmonics (1/3 3f, 1/5 5f etc) which are not actually present in the voltage waveform, so if there is any harmonic current at these frequencies it will give corresponding spurious terms in the expression for power. This is probably addressed in the paper above but I confess I have not actually looked it up.

I have found the cause of my 5% error. I originally analysed the effect of crydom current shape but only the up to half power. Up to this point the demodulator gives a higher house power than actual so no problem I am not after 100%. I incorrectly assumed that this would be the peak but having simulated the full range the current shape gives a 7% under power. Limiting the integrator dc gain on a single ct implementation fixes the problem.
The multiplier arrived today and I have tried it out. Performance is as you described. I will be testing it over temperature in the next few days where I expect to have serious problems if its offset spec of 50mV is real. I should be able to compensate the circuit fairly easily. On the single ct after some analysis the scale error of the device will not matter as the peak value is not high when the currents are balanced. I too get a 100Hz buzz but no interference. Even with a multistage filter the current rise time is very high I think a different approach may be required to mitigate this effect.
 
Last edited by a moderator:
Interesting thing, that power halver, though I'd wait to see how much the 3kW one is as it would mean the standard/existing element could be used......

I have used a single diode out of a MB356 BRIDGE RECTIFIER 35 Amp 600V (£2.79 posted from polarity_electronics_uk on ebay ) to halve my 3Kw immersion load. Its AC input feed is relay switched in with a wireless remote when the output from the PV exceeds fixed amount.

It gets warm but not hot as it's only having to dissipate < 10W so is mounted in a double wallbox with cooker isolating fuse/switch.

A similar unit could be used to half feed a 750W oil filled radiator.

Will try the CT differential phase control technology mentioned elsewhere when I have time...

d.
 
Last edited by a moderator:
You mean a lower power heating element? Problem with those is that you then lose the versatility of the high power original if you need it. Advantage over diodes is that it doesn't mess up the mains current waveform.

A tip to delleray: use two diodes in parallel from the bridge (connect both AC terminals together) to reduce heat dissipation and increase reliability marginally.
 
Oh you mean this? As you say, it only monitors PV power rather than exported power, so is really not a satisfactory solution because as soon as you turn on a kettle you will start to pay for the immersion heater.
 
Yes. they are good enough to use when the house is in standby - When no one is in the house. Working fine for the last one month with my install. It leaves 500W for the in house use - So will turn on the immersion automatically at above 1.5 kW PV production. I'm getting full tank of 60C ho****er even in feb with this setup- boiler hardly runs.

I have a immersion switch as well, will turn it off during weekend when washing machine is on.
 
A bigger tip to delleray: it's illegal to do this because it puts a large direct current back down the mains. Someone else has posted the actual permissible limits, but you can be sure an immersion heater exceeds them by a very wide margin.

It's also dangerous for you because ordinary Residual Current Devices (ELCBs) don't work with a large d.c. component to the current, so you and your family will not be protected against electric shock any more.

For both these reasons it is preferable to use a step-down transformer e.g. a 240/110V site transformer to reduce the power to the immersion heater.
 
Hi all,

Found this site via a PV thread: my eyes did glaze over as I waded thru all 44 pages.

I'm not an electrician or an engineer, nor am I interested in this field - I just want to use my free electricity to heat my hot water (apologies to those who think that's not green). However ...

it would seem to me that if a device monitored the pulse on the import meter so that it only switched on the immersion circuit when you're NOT importing, that would allow any excess PV electricity to be diverted to the immersion. (or is that too simple an idea?).

BTW, echase, claims for your system appear interesting, but there's too much secrecy to give me confidence - even your customers on this board are not willing to discuss something a simple as the price??

Would be good to hear about Sparqui's progress with that solution (post 338).
 
Last edited by a moderator:
Hi all,

I'm not an electrician or an engineer, nor am I interested in this field -

BTW, echase, claims for your system appear interesting, but there's too much secrecy to give me confidence - even your customers on this board are not willing to discuss something a simple as the price??
QUOTE]

This forum is mainly for people interested in sharing design ideas for solving this issue. I respect that so don’t clog what is already a very long and interesting thread with adverts for my design and I ask people who have my units not to do so either. Happy to receive Private Messages on it though and give out testimonials that way. I supply people with at least some electrical or electronic engineering expertise. It’s not for the beginner.
 

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
441
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
383
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock