I’ve been looking for the right answer and just can’t seem to find it.
I had an induction hob installed by a certified electrician, and there are no apparent problems so far, however, it is installed on the CU, RCD and upstream with a RCCB with no MCB,
I’m just not 100% sure if it’s the safest way to install it, I would personally think that would be safer on an RCBO or on a MCB, I’m not worried about overloading as it’s on a 10mm2 cable, 40a RCCB and the unit draws a max of 25Amp, I worry more about the fact that the RCCB will not protect on short circuit.
I appreciate any feedback or comments.
Thanks
 

Attachments

  • 9683AA16-5980-4207-88CA-83C96C6EF8C1.jpeg
    557 KB · Views: 84
Can't be certain but it appears the RCCB is fed from the top left 32 amp MCB.
That board is a bit of mess to say the least.
Thanks for the comment, yes not state of the art.. it’s a 20 years old CU. The RCCB is feed from the busbar from the RCD as all the other MCBs on the busbar, I think there is no problem there. Question is about the RCCB being safe or not without an MCB.
Thanks
 
Thanks for the comment, yes not state of the art.. it’s a 20 years old CU. The RCCB is feed from the busbar from the RCD as all the other MCBs on the busbar, I think there is no problem there. Question is about the RCCB being safe or not without an MCB.
Thanks
In that case, the circuit fed from the RCCB has no overcurrent protection.
 
OP, what made you look at how the electrician had wired the cooker into the consumer unit?

Did you get an installation cert?

And yes, fundamentally every circuit needs over current protection of some sort.
 
OP, what made you look at how the electrician had wired the cooker into the consumer unit?

Did you get an installation cert?

And yes, fundamentally every circuit needs over current protection of some sort.
my interest and curiosity for electricity and the safety of my home and family, do that suffice?
no cert provided..... cowboy, I called many snags on the electrician alone... I'll spare you the details, just to say the cover for the connection under the hob was found on a drawer... then I saw the wires exposed...
 
Thank you all for your comments, very much appreciate that you took your time to give your opinion on what seems to be a hot mess of a CU, I kind of knew that, the whole house was built on a weekend during the boom in Ireland so no surprise there. I just want to focus on having the correct protection, for now, aesthetics is not my main concern right now.
What I take from all your comments is that the RCCB where the Induction hob is should be an RCBO, and that the current RCCB does not provide enough protection to the hob or the circuit and it could be an electrical hazard?
 
On the face of what is presented above I would say the OCP is not achieved with the installation method used. What might be the consequences of this? In terms of overload it is not a problem as it is a fixed resistive load and can only achieve a fixed amount of load. In the event of a short circuit where the load may well exceed the CCC of the cable due to the fault current exceeding by many multiples the CCC of the cable. Therefore the cable may melt/explode causing danger of fire. It would then be prudent and indeed required to arrange the appropriate protection for the cable. Ensuring the operative engaged is properly qualified to undertake such work. The chance of a short circuit while being quite remote is nevertheless important to have remedied.
 
On the face of what is presented above I would say the OCP is not achieved with the installation method used. What might be the consequences of this? In terms of overload it is not a problem as it is a fixed resistive load and can only achieve a fixed amount of load. In the event of a short circuit where the load may well exceed the CCC of the cable due to the fault current exceeding by many multiples the CCC of the cable. Therefore the cable may melt/explode causing danger of fire. It would then be prudent and indeed required to arrange the appropriate protection for the cable. Ensuring the operative engaged is properly qualified to undertake such work. The chance of a short circuit while being quite remote is nevertheless important to have remedied.
thank you very much for your comments and advice, much appreciated.
I've decided to keep the RCCB turned off while not in use just in case.
I will make sure a reputable certified electrician does the job... possibly replacing the whole CU and new more modern type B breakers with 6ka capacity class3, instead of 3ka, although here in Ireland that it's extremely hard! not to say almost an impossible quest!
 

Reply to Induction hob correct install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
950
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
441
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hii sorry for the post in advance because it’s basically a huge winge. I’m a 31 year old female who decided to change career in 2019 (ish I...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock