do you mean with values ?

Typical example are transformers, big inrush until the field gets established.
Often worse than motors size for size and they dont care whether there is any load.

Manufacturers give the data for inrush curves so you can match it to a breaker
 
No rob what it is a Madrix main switch with different settings on its a 200a switch set at 1 which is 200a but another dial next to it is set at 5 Madrix tech people said this is for your inrush current I'm awaiting an email of them explaining in better detail
 
In-rush or start up current is the extra current drawn to start certain items of equipment, such as flourescent lights, discharge lighting, DOL motors, welders, etc.
A setting of 5X the overload current seems rather extreme.
I'd expect 1.5X - 2X, hence type C and D MCBs.
 
Thermal O/L has a time curve the same as you would find on a domestic MCB.
Magnetic O/L is for short circuit protection. It needs to operate fast in the case of a S/C but must allow the magnetising “inrush” current for inductive loads without tripping. It’s a juggling act between sensitivity to short circuit and the let through for inrush.

Several years back I changed a burnt out 300Hp motor, the company policy was that any replacement had to be a high efficiency motor. High efficiency = higher inrush. First test run (direction check) with no belts on the pulleys, all OK. once the belts were put on, Oh dear, the 400A MCCB tripped immediately on instantaneous O/L. We had to fit a new MCCB that could withstand 8X current.
Final settings were I-th .95, I-in 7X. So I-in = 2800A
 

Reply to Inrush current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
790
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K
Hi, We have a 4kW PFC we are doing. (100-265VAC, +/-180V) The input is a Boost PFC...it has 4.3mF of output capacitance. We want to inrush into it...
Replies
12
Views
1K
Hi Everyone, My first post here, just a simple question. I currently get all of my work through word of mouth and contracts that I have...
Replies
14
Views
652
hi all, What are your thoughts on how the 6231 cables been terminated? Will aluminium cause eddy currents? Thanks
Replies
37
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top