Discuss Installation reference method B in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi Guys

Is there a reason why installation ref method B (in conduit or trunking on a wall) not listed as an allowed installation method on the maximum cable length charts (table 7.1)?

Regards
 
Because it's a quick reference for basic circuits using the most common installation methods, it's not a difintive guide and for anything else you have to wokr it out yourself.
 
I wonder if you would be so kind to help me.
I have 5 cables that will require to be ran in about 3m of trunking across a garage wall. The cables are 4 x 2.5mm (one ring 32amp cb, fridge radial 16amp cb and oven radial 20amp cb) and the other cable is 4mm utility radial 32amp cb.

Is it OK to run these 5 cables together (concerned with them all being kitchen related ie higher current) in the trunking and if so what size would you recommend?

Regards
 
I wonder if you would be so kind to help me.
I have 5 cables that will require to be ran in about 3m of trunking across a garage wall. The cables are 4 x 2.5mm (one ring 32amp cb, fridge radial 16amp cb and oven radial 20amp cb) and the other cable is 4mm utility radial 32amp cb.

Is it OK to run these 5 cables together (concerned with them all being kitchen related ie higher current) in the trunking and if so what size would you recommend?

Regards
The clue is in the last seven words of your first reply above - we have a soft rule on here to not do people's homework for them. However, as you seem to be clued up enough to know where to look, why don't you have a go and then post up your workings, that way we can actually help you and others learn. And hey, you might get it right first time anyway!
 

Reply to Installation reference method B in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, How do you think reference method and type of wiring for flat twin and earth in non-metallic conduit will be : just C and B...
Replies
2
Views
206
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
576
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Morning! Would someone please mind checking the big brown book for 1.5mm flat sheathed cable, ref method B, CCC? Page 456 from memory. Only have...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock