Discuss Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie


Haha the PS bit made me chuckle
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie

Your added problem with regards to the cable size is that it will have to be based on the neutral current unless you can perfectly balance the phases. So you might end up going up two sizes anyway.
 
A high spec 5/6 bed house (the sort of house than might be down a 100m drive) will often have a lot more appliances than typical.

I've worked recently on one such house, e.g. the kitchen has 2 built-in ovens, built-in warming drawer, built-in steamer, built-in microwave, 6-ring hob. The plant room has a couple of big water tanks with backup heaters in case the gas boiler fails. Every bedroom has an en-suite (though depending, the showers might not be electric). It needed a lot more than 100A.
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie


Sorry Martin that was my bad - I didn't segregate my post, its done now though, I should have multi-quoted :blush5:
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie

Yes 100A single phase would almost certainly be fine, but that is not the same thing as 40A three phase when the installation will be made up of single phase loads.
 
Your added problem with regards to the cable size is that it will have to be based on the neutral current unless you can perfectly balance the phases. So you might end up going up two sizes anyway.

Do you have any technical backup to that statement? Because it sounds somewhat fishy on the surface of it when you consider that no imbalance situation will cause the neutral current to be higher than any of the phases.

The only time neutral current will become a problem is when third order harmonics are present
 
Do you have any technical backup to that statement? Because it sounds somewhat fishy on the surface of it when you consider that no imbalance situation will cause the neutral current to be higher than any of the phases.

The only time neutral current will become a problem is when third order harmonics are present

I have recently returned from the pub and my statement is based on information gathering dust in the dirty crevices of my mind. I’m back at work tomorrow, so will look it up then. From memory it’s one size up for a 20% imbalance and two sizes up for a 40% imbalance.
 
I have recently returned from the pub and my statement is based on information gathering dust in the dirty crevices of my mind. I’m back at work tomorrow, so will look it up then. From memory it’s one size up for a 20% imbalance and two sizes up for a 40% imbalance.

I think you are getting confused with something else, there is no such thing with basic three phase circuits.
 
Either way, I would be funny as hell to watch him wrestle with a 185mm into a 60-80A main switch.:biggrinjester:
 
Either way, I would be funny as hell to watch him wrestle with a 185mm into a 60-80A main switch.:biggrinjester:

It's ok, he's using a hager switchfuse, everyone knows they are the best of the best when it comes to industrial switchgear and ability to terminate oversized conductors !


Methinks the op may not be used to working with the larger sizes of cable, hence the rapidly reducing design current through the thread.
 
A high spec 5/6 bed house (the sort of house than might be down a 100m drive) will often have a lot more appliances than typical.

I've worked recently on one such house, e.g. the kitchen has 2 built-in ovens, built-in warming drawer, built-in steamer, built-in microwave, 6-ring hob. The plant room has a couple of big water tanks with backup heaters in case the gas boiler fails. Every bedroom has an en-suite (though depending, the showers might not be electric). It needed a lot more than 100A.
Yes SJD but we are still working on diversity, any ones guess as to how many appliances are fully loaded at the one time
 
It's ok, he's using a hager switchfuse, everyone knows they are the best of the best when it comes to industrial switchgear and ability to terminate oversized conductors !


Methinks the op may not be used to working with the larger sizes of cable, hence the rapidly reducing design current through the thread.

What I can’t understand is why they couldn’t build the house nearer to the services.:biggrin:
 
Thanks for your replies.
Here's my calculations based on 80 amp 415v supply. Distance 135m. Buried in the ground
Total load 44.34Kw
Consumed Load in KVA divided by power factor 44.34/0.8 =55.42
Full load current 55.42x1000 / 1.732x 415
55,425 / 718.78 = 77.10 Amp
Ground temp correction factor 0.95
Soil correction factor 1.05
Cable depth correction factor 1
Cable group correction factor 1
Total derating factor 0.99
50mm 4 core cable current carrying capacity= 116 amps
Resistance =0.8
Reactance = 0.14
Total derating current of 50mm 116 x 0.99 = 114.84
Volt Drop
1.732 x 77.10 x (0.8 x 0.8 + 0.14 x 0.6) x 135 x 100 / 415 x 1000 = 1.95

Haven't done these sort of calculations for a while so sorry if there are any mistakes
 
Or more to the point, how it can make more sense to install this distribution circuit than to have the service installed at the house in the first place?

It’s to make it easier for the local scrap cable recyclers to strip out the tails and leg it before the owners can make it down the drive.:angel_smile:
 

Reply to Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
303
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
997
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
640
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
894

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock