You won't get three or four pole rcbos for that board.How about a 3 pole RCBO Westward?
Haven't found one yet though!
Discuss Installing a 3 phase rapid EV charger? in the UK Electrical Forum area at ElectriciansForums.net
You won't get three or four pole rcbos for that board.How about a 3 pole RCBO Westward?
Haven't found one yet though!
A triple pole RCBO would be no use for an EVSE installation.How about a 3 pole RCBO Westward?
Haven't found one yet though!
I have a job using these boards currently. Do they take the Schneider multi 9s? I assume they do but would rather be sure before buying ten mcbs.If there are three spare ways in the Merlin board then yes take the circuit from there but you will have to fit a separate rcd as you won't get a four pole rcbo for that board.
Completely agree Risteard, but in this case it is just feeding a commando socket so would be ok. However, I've bought a 4 POLE RCD combined with a commando socket and will use a 3 pole MCB in the CU.A triple pole RCBO would be no use for an EVSE installation.
Ideal.Completely agree Risteard, but in this case it is just feeding a commando socket so would be ok. However, I've bought a 4 POLE RCD combined with a commando socket and will use a 3 pole MCB in the CU.