Hi Hope someone can help answer below ?

I have had a few views on how best to terminate our marshalling boxes for instrumentation panel wiring. As you will be aware the instrumentation wiring has screens which are either individual or overall screens in 20 pair cables. Now on some jobs that I have been on when the cables enter the marshalling boxes they take off the inner insulation say 25mm as it enters the enclosure then put a piece of self amalgamation tape over the crutch of the cable and sleeve the overall screen. The foil of all the individual screens is kept on and dressed up to the terminations then the foil is stripped off 30mm from termination then self amalgamation tape over then connect the pair and individual screen into the terminations, screens are sleeves also, the foil has plastic also over the paired cables before being stripped at terminations. Also seen where they strip all the foil off right down to the crutch then self amalgamation tape over each of the pair and then dress up. I would just like views on what others do and if it is just down to engineering preference?
 
I don't like self-amalgamating tape. I put silicone sleeving over the drain wires, then secure with expandable (Hellermann) sleeves at the crutch and the end of the pairs. If the foils are at risk of damage or it is important to prevent contact with each other if the melinex film gets breached, I over-sleeve the pairs. Ideally, when finished it should be impossible to bridge together or make contact with screens at any point, even if you probe the bundle with a meter probe.
 
I would agree with @Lucien Nunes that self-amalgamating tape is not a good choice here. My usual approach is heat-shrink, but you need to take real care as some cable's insulation will melt at temperatures not much over what is needed to shrink the sleeving.

Also check with the designer if there is any need (or definite need not to) attach any overall screening braid to any metal box entry via a suitable gland for good EMC performance.
 
Thanks for the replies guys, yeah just seeing which way other people do it, the foil is all protected by the wrap around plastic, then hellermann at just before entry in to terminals, I think it looks neater this way and also saves time in stripping all the foil off when inside floor to ceiling marshalling boxes, just didn’t know if there was any engineering reason behind it ? Why lads do it differently ?
 

Reply to Instrumentation marshalling boxes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
940
Firstly, I hope it is ok to discuss the wiring of speakers here. TBH my ignorance in all things electrical knows no bounds, and I am guessing it...
Replies
31
Views
3K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock