Discuss insulation resistance testing stanless steel in the UK Electrical Forum area at ElectriciansForums.net

i=p/u

-
Arms
Reaction score
801
in a cafe at present working and is a load of stainless steel in one corner for washing up etc..

i want to do a test to see if needs bonding

im nearly certain i I r test from earth isco to stainless steel in question and test @ 500vdc and if under 22k ohms it should be bonded,

is this info in big green book(bs7671) all electrical equipment in this area is ip44 rated.. any guidance welcome
 
What makes you think the stainless steel is an extraneous conductive part? Is it bolted into the ground or in some other way significantly "earthy"?
You are correct about testing though, test from earth MET (remove all parallel paths) using IR tester at 500 volts, if the result is less than 22k ohms then bond it!
 
so turn of main supply, remove earthing conductor and test accordingly, all im doing is new lighting and like for like fittings and noting anything that doesnt look right. i.e ring ciruit on 40A breaker
 

Reply to insulation resistance testing stanless steel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Greetings! Newbie here! We have 3 phase installation in our Lighting dimmer rack. During Insulation Resistance testing on Earth-Nuetral, readings...
Replies
20
Views
5K
On initial verification of new installations I have been having a hard time with insulation resistance. With RCBOs, fixed LED luminaires...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock