I had a quick job yesterday where the customer said he lost power to some kitchen sockets, I went round and he had an old wilex board with rewireable fuses. All the sockets in the house were on two 30A fuse wires. Most sockets in the kitchen were in a ring on 1 and the rest of the house must have been on the other (oddly there were some sockets in the kitchen on the other too). I didn't do any testing on the other circuits and the fuses were fine.

Basically all I did was remove the 5 affected sockets and check the wiring in them, they were all fine apart from one where some of the cables were loose, I reconnected it and did an IR and all was fine. I replaced the fuse and all the sockets were working. Even though the wires came out they only came out when I removed the socket from the pattress but I thought that must have been the fault.

Except they rang me this morning to say it has happened again and it was when the dryer was on, they also said it happened last time when the dryer was on.

How can they have a complete loss of power (less than 1v measured) on these sockets if the wiring is good and the supply is good? Bearing in mind I managed to remake the circuit just by removing some sockets and removing a fuse then replacing them. I just want some ideas of where to start when I go back tomorrow. All I can think of IF the wiring is definitely good is some kind of thermal cutoff switch hidden away somewhere. I think that's pretty unlikely - could there be some connection issues in the old board?
 
Well no, I didn't see the point.

Their circuits haven't been touched for years. When I found the fault in the socket and when I replaced the fuse the circuit came back up - I saw no reason to continue with fault-finding.
 
Well no, I didn't see the point.

Their circuits haven't been touched for years. When I found the fault in the socket and when I replaced the fuse the circuit came back up - I saw no reason to continue with fault-finding.
There is fault finding and Testing
 
Well no, I didn't see the point.

Their circuits haven't been touched for years. When I found the fault in the socket and when I replaced the fuse the circuit came back up - I saw no reason to continue with fault-finding.

Fault finding can be difficult and time consuming. You can try and wing it, and you might be lucky.

The alternative, is to test the circuit from the beginning, as if it was new to try and locate the fault. As it is, you don't know what the fault is, other than it is an intermittent fault, resulting in no supply.
 
So the recommendation is I just start the fault-finding from the start? I was looking for some more targetted advice, I don't want to be here all day doing continuity checks on every length of wire if I don't have to. Obviously I do want to do it properly though.

EDIT: I was just hoping that someone might have had a more simple solution they may have come across in the past.
 
Fault finding can be difficult and time consuming. You can try and wing it, and you might be lucky.

The alternative, is to test the circuit from the beginning, as if it was new to try and locate the fault. As it is, you don't know what the fault is, other than it is an intermittent fault, resulting in no supply.

You're not kidding. I put in a CU for a customer last week and I had 0.1MOhm IR L-N on an unidentified circuit (they all were unidentified). I had the washing machine out, the dishwasher, dryer, about 15 sockets and I couldn't find it. Turned out to be the light in the cooker hood (not the light itself, the T&E leading to it that I couldn't access). You live and learn - check the easy stuff before you go pulling out cookers, 4 hours wasted :(.
 
So the recommendation is I just start the fault-finding from the start? I was looking for some more targetted advice, I don't want to be here all day doing continuity checks on every length of wire if I don't have to. Obviously I do want to do it properly though.

EDIT: I was just hoping that someone might have had a more simple solution they may have come across in the past.

It sounds like you may have a lose connection, you could check at the socket used by the tumble dyer, but the fault could be elsewhere. As you've found another socket with lose connections, I would recommend you start at the beginning, starting with continuity of ring final conductors, and analysing the results. Otherwise, as you've found out, you've think you've rectified the fault, when in fact you've rectified one of several faults.

Alternatively, you could invest in a crystal ball.
 
It sounds like you may have a lose connection, you could check at the socket used by the tumble dyer, but the fault could be elsewhere. As you've found another socket with lose connections, I would recommend you start at the beginning, starting with continuity of ring final conductors, and analysing the results. Otherwise, as you've found out, you've think you've rectified the fault, when in fact you've rectified one of several faults.

Alternatively, you could invest in a crystal ball.

OK, seems fair enough.
 
YES, proper testing can be long and painful. Usually split circuits in half and work from there. The last one I had a couple of weeks ago took nearly all day !!. Kitchen fitters had covered up box and cables, pushed in cables and shorted to side of box, work done 7 yrs ago !.
Needed cupboards removing from wall to find fault !.
 
This one was hidden, about 50 years ago;
Socket1.jpg Socket2.jpg
 
If it were a lose connection on a ring final I would not expect several sockets to be non functional unless they are a radial.
 
Unless its only 'lose' when the tumble dryer gets going :)

Edit; the OP will only find out, when it's tested properly and from the begining
 
If it were a lose connection on a ring final I would not expect several sockets to be non functional unless they are a radial.

Well perhaps there are several loose connections, and what is supposed to be an RFC has already one or more breaks, possibly intermittent ones. When at least two connections go open circuit on L or N, the power is lost?
 
I would suggest that end to end testing of the ring to start with would be a good idea.
Losing power on a ring is not common without something else wrong.
I would suspect there was a joint overheating somewhere on loading the circuit and that the ring had been broken at some point, or it is a lollipop ring,but that is not so from your description of the circuit.
 
Back to basics is the place to start...

Just done an EICR where a few sockets worked on and off - rocking my tester in the socket confirmed, in each case, that the sockets were knackered.....
 
Back to basics is the place to start...

Just done an EICR where a few sockets worked on and off - rocking my tester in the socket confirmed, in each case, that the sockets were knackered.....
"Rocking my tester in the socket" what does that mean?
 

Reply to Intermittent sockets, wiring and fuses fine in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
587
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
593
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
873
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock