Was called out to a site where an employee has recieved an electric shock when turning on a light.

When I isolated and removed the switch the cause was immediately apparent.

20190913_191213.jpg


It was a metal surface box and mettal clad switch, the back box had been drilled through the back for a 20mm conduit but never used, favouring a top entry using condit.

Basically the rear entry hole had left a nasty burr which over 30ish years has slowly cut into the line conductor until yeasterday when someone operated the switch and wallop.

The guy had a lightly singed finger and attended hopital for a check up but was otherwise ok.

Fortunately the circuit had been put on an RCBO due to an addition, although not necessary at the time.

Amazing how such an issue can sit there for so long before zapping someone.
 
I wonder if the person who got the belt happened as they put pressure on the switch pushed it back just enough so the live conductor got squashed against the sharp edge and bang.
 
So the question is, what was the shock voltage and duration? The box must have been reasonably well earthed to produce a splash like that, in which case the RCBO should have responded quickly. And a short duration shock of modest contact voltage, although nasty for a moment and a potential trigger of a cardiac event, is unlikely to cause a burn.
 
Did the finger actually get burned, or did it get a bit of a black mark on it?

Is that black mark definately the result of this incident or could it be left from an older incident? I don't think I've seen a black mark like that on a circuit with 30mA rcd protection before, they usually disconnect long before enough current flows to cause that.
 
I wonder if the person who got the belt happened as they put pressure on the switch pushed it back just enough so the live conductor got squashed against the sharp edge and bang.
From what was said that's exactly what happened.

Makes yoi wonder how many times that switch has been pressed in it's lifetime.
 
From what was said that's exactly what happened.

Makes yoi wonder how many times that switch has been pressed in it's lifetime.
Has the person concerned ever had an electric shock before? I’m wondering if he was just shocked by the flash and bang thats enough to scare you but as long as he’s fine and well that’s the main thing lethal industry we are in and hope it doesn’t scare him off.
 
Has the person concerned ever had an electric shock before? I’m wondering if he was just shocked by the flash and bang thats enough to scare you but as long as he’s fine and well that’s the main thing lethal industry we are in and hope it doesn’t scare him off.
No, i think he got a propper crack, he not a spark but an employee at the business concerned.
He certainly is a bit wary of switches now.
 

Reply to Investigated an electric shock today. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch...
Replies
44
Views
8K
Hi everyone, Not an electrician myself, but seeking knowledge, a second opinion and/or advice on the necessity to take action. Hope this is the...
Replies
32
Views
17K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock