Hi all,
This morning I visited a new client who needs me to find out why there bills are so high.
At the moment I can only give a quick rundown of the installation as it was just a general chit chat about the issue. I will be going back to do some proper investigation in a week or so.
This is an old manor farm with the main house having been extended along with an attached barn conversion which is their main living space. 3 story's including the loft conversion so quite a considerable space. They have a 3 bed cottage ( Detached )on the land along with stables a plant room and a wooden barn converted for parties in an L shape. So they called me because they are getting extremely high bills. The 2 that I saw was 1 for last 3 months and 1 for the previous 3 months. The latter was for £4100 and the other was £2700. I did get a quick look at a couple others and they were similar costs ranging anywhere in between.
Firstly can anyone say whether this is normal for a house of this size when they have assured me that they don't use the emersion heaters as they have 2 big oil boilers in the plant room.
Wet underfloor in the new half and the barn end and radiators in the old part of the house.
Also my first thoughts are that I need to familiarise myself with the wiring of the entire installation so I can eliminate circuits one by one. Any advice is welcome as always.
 
Last edited:
Smart meter been fitted?

find out if its single phase, two phase, or single phase.
Rent an an energy consumption monitoring unit which will simple have clip on CTs.

you could have fault current flowing through a high impedance path with would be seen as a large load and not trip any protective devices, its possibly a TT system you have on site
 
find out if its single phase, two phase, or single phase.
Rent an an energy consumption monitoring unit which will simple have clip on CTs.

you could have fault current flowing through a high impedance path with would be seen as a large load and not trip any protective devices, its possibly a TT system you have on site

It is 3 phase main DB in the plant room.
3 phase DB in main house which had been completely redone around 2008.
Single phase CU in party barn.
Single phase CU in cottage.

Was thinking something similar myself about current flow but not sure where that current would be flowing.
 
This is an old manor farm with the main house having been extended along with an attached barn conversion which is their main living space. 3 story's including the loft conversion so quite a considerable space. They have a 3 bed cottage ( Detached )on the land along with stables a plant room and a wooden barn converted for parties
what do they except with that to have free electricity.
may be some one leaving a light on to longer!
 
what do they except with that to have free electricity.
may be some one leaving a light on to longer!

Do you think that £4100 is acceptable for a quarter when they know they don't use a lot of electricity themselves. Clearly they don't want free electricity and I can assure you they quite well off but why would anyone pay for something that they are not using regardless of how much money they have. Really don't see the point in your comment.
 
Let's see what kind of load you need to rack up those bills.
Typical leccy price 12p/kWh
Total consumption over 6 months (4100+2700)/0.12=57MWh
6 months = 24*365/2=4380 hours.
Average continuous load 56666/4380=12.9kW.

Whatever you use electricity for, by the time the energy leaves your house it's almost entirely converted into heat (unless you live in a pumping station or mine headworks). Therefore if this consumption is real, there must be the equivalent of 6 1/2 2-bar fires of heat being pumped into the house all the time. Unless some of the long-hour load is aircon of course. If you were supposing half of the consumption were due to a fault, whatever makes up the resistance of the fault (earth rod, someone suggested) would be getting as hot as two immersion heaters on full whack could make it (i.e. not cycling on their thermostats, elements on full all the time).

It seems unlikely that so much energy could be dissipated unseen in a domestic environment, so either they have a generally high load (e.g. sneaky extra electric heaters and/or aircon and poor thermal insulation, lots of inefficient decorative tungsten lighting on 24/7, all their considerable space in use much of the time) or the readings are out. Unless, of course, someone has set up a hydroponic cultivation department.
 
upload_2017-7-1_19-20-25.png
may be you need this guy!
 
I will be doing as advised earlier and fitting an energy monitor. Might do a week on the main DB and then a week on each sub mains DB. Not even sure if the other 3 subs come from the main DB as the cottage is close to the main house so may be fed from there. Will know more after my initial investigations.
 
Thinking may get away with a clamp meter as I've just seen the price of these machines. Just check current flows to each DB and see which one has got an unusually high current flow.

That will only tell you the instantaneous current flow, it won't tell you anything about the average demand.

I would say the first thing to do is contact their electricity supplier (the meter operator, not the DNO)
I believe they are required to investigate if there is a query about the bill.

As mentioned above if the bulls are estimate s this may be part of the cause. Have a look at previous bills to see if there is a gradual increase over the years or if this is a sudden jump up.
 
The expense of a data logger at this stage seems a little excessive, a basic clap meter will allow you to identify the circuit (s) with high loadings. If you can't identify an issue with this method then a data logger might be considered a robust method of demonstrating a meter malfunction to the DNO.

However, Do DNOs offer meter calibration testing - only charging the customer if no fault is detected.

Let us know how you get on.
 
I bought myself the Fluke 1730 Energy logger and it's already paid for itself at nearly 2k it wasn't a knee jerk purchase but I've had it hired out nearly every week since I bought it so it is now making money every week.
They are well worth the money, simply input the unit price for electricity and it will work out exactly what your installation is costing.
The logging period can be set from 10 minutes to 3 months and at the end you can print off the results or email them direct to your customer, equally you can drag snapshots off of it with a memory stick while it is logging.
We also use it to carry out load tests on machinery, some of our customers like to know what some of their large machines are costing to run for help with working out production costs.
 
Problem with such vague posts such as these as we are all guessing.

OP - you need to ask the customer to get out ALL their old bills, and

1. look at the amounts due
2. they need to check if they are estimated or proper readings
3. also log the consumption per quarter

- only then can they actually compare apples with apples.
 
with that amount of current flowing it shouldn't be hard to find.

Indeed not. If half the bill is wastage via leakage to earth, the L-E insulation resistance would be 8.2 ohms, so about a ten-millionth of what you might expect on a domestic system. You would want to search for it with a continuity tester, not an insulation tester, as that would just read a string of zeroes - 0.000008 Megohms if it had that many digits. Somehow I doubt this as the cause - the fault would be dissipating the heat of over three 2-bar fires, which I can't imagine XLPE SWA withstanding for over six months. The ground would probably be steaming! Although anything is possible until you get some data.
 
may be the electricity company they get
the supply from need to be involved and ask them.

Think this is the most sensible suggestion to check first. Why pay hundreds of pounds getting an electrician to check if there is something wrong with the electrical installation, if they've got some dodgy meters or readings.

Get the fuel supplier to verify their meters.
 
Think this is the most sensible suggestion to check first. Why pay hundreds of pounds getting an electrician to check if there is something wrong with the electrical installation, if they've got some dodgy meters or readings.

Get the fuel supplier to verify their meters.
And if the readings are correct?
 
I would say most are where the price goes up, the direct debit doesn't, the consumption goes up..... Then the supplier does a meter reading...... Then the payment jumps....
 
well you can do some very simply thing like check the electrical meter readings on a daily basis, record these and see if there is a spike, you could do this over the Phone with the customer
then see what they are paying for a KW hour, normal about 13p. ish but it may be cheaper.

but if the customer are well off then look at the energy tracking devices which are out there a couple of hundred quid. these are better as they will record the power consumption and give you an idea if its a steady consumption or a spike at a certain point. These can visual display the Data in graph form for easy of understanding.

if its a steady consumption then get a clamp meter out and check all the circuit to see whats going on and which circuit is using the power.

hope that helps. goggle is a good tool

here a web site which offer some tracking

Tracking Your Energy Use | Home Power Magazine - https://www.homepower.com/articles/home-efficiency/electricity/tracking-your-energy-use
your need to find a 3 phase meter,

I think £4100 is quite a bit, A very rough calculation, if they paying 13p a KW hour ,
then they using something like 31,538 KW Hours ,now if that's a quarter then there about 11,500KW hour a month and about 350KW hours a day. that mean they are using 14KW every hour.!
 
Has your client checked that the readings on the bills match the readings on the actual meter(s)? Wouldn't trust suppliers further than I could through them...
 

Reply to Investigation on massive electricity bills in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
512
Just under 2 years ago my central HVAC died. I wanted to go with a heat pump because the only appliance in the whole house that used natural gas...
Replies
0
Views
918
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top