Discuss Ipfc/Ipsc measurement at 2nd distribution board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

filo

-
Reaction score
0
Hi,
My first post - hope someone can help.

I need to test the prospective fault current at a garage consumer unit. The unit is supplied from an RCBO in the main consumer unit. I intend to carry out the test at the incoming terminals of the garage consumer unit switch with everything switched off except the main switch and the RCBO on the main consumer unit.

My question is this:
Is this likely to damage the RCBO? If so how should I carry out the test - temporarily bypass the RCBO? or can the test be avoided by doing a calculation (I have the prospective fault current at the main board and the R1+R2 of the distribution circuit).

Any clues would be appreciated.
 
You can test the pfc on a no trip setting or test the Zs at the cu on a no trip setting and calculate.
 
Thanks - will try Ipfc test - think my meter is automatically 'no trip' although it hasn't always worked.

At the risk of sounding a bit dim - would I be right in saying that the prospective fault current is likely to be significantly lower than at the main consumer unit because the R1+R2 of the distribution circuit is of roughly the same order as the Ze?
 
Yes the further you go from the origin the lower the pfc will get.
 
If you don't have a no trip function on your tester you can still get a reading for the the Zs at the submain.

Isolate the rcbo at the CU which is supplying the submain
link out the line and earth at the submain
At the main CU, test with your earth loop impedance tester, black probe to the isolated side of your rcbo and red probe at incoming line to rcbo or main switch. Your reading will be the external loop impedance for the submain. Divide that into your voltage and you have your pefc for your submain.
Make sure you remove the link at the submain before energising your rcbo.:)
 

Reply to Ipfc/Ipsc measurement at 2nd distribution board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
641
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
Hi, I've got to put in an additional consumer unit into quite a large property and rather than daisy chaining them back to a single MCB in the...
Replies
8
Views
4K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock