Discuss iPhone chargers. To test or not to test? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

What are you ACTUALLY testing with a PAT tester and a charger?
As per @marcuswareham, the rather important insulation between input and output. Some low-cost non-OEM chargers have design and/or construction flaws leading to only the barest minimum of basic insulation. E.g. we have seen units with 1mm PCB track separation, which is an unacceptable creepage distance but it works so they do it. Others rely only on enamelled winding wire on the transformer to achieve separation, the inter-winding taping or ELV secondary over-sleeving having been omitted. Even where the design is sound, in cheap units with poor manufacturing QC there could be any kind of assembly error such as the input pin flylead trapped against an ELV solder joint, or the secondary transformer leadout snagged around a live component.

Genuine OEM chargers are in a different league of quality when new, but can still have drinks poured over them, or get dropped down the stairs...
 

Reply to iPhone chargers. To test or not to test? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
553
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
966
Hi all, Just looking at starting some testing since newly qualified, don't know if this is a stupid question or not. Is there an allowed...
Replies
5
Views
680
Currently I’m using freeagents platform for invoicing and it’s decent and gets the job done but it’s lacking a few features. Firstly I want to be...
Replies
12
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock