Currently reading:
IR method 2

Discuss IR method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Tim

-
Reaction score
66
Hi guys,

What plug in equipment, if any would show a dead short when doing an ir test?

I have the line and neutral connected together and testing between that and the earth bar.

The circuit was energised and working fine on arrival (doing an eicr) so it cant be an actual dead short or the mcb would have tripped.

The circuit im testing is a 16a 2.5 radial that feed sockets in various rooms some of which are ceiling high with crap so something could be plugged in and i wouldnt even know.

Cheers,
Tim
 
Could be anything, usuall what I find is fused connection units supplying deaf loop, intruder alarms, small P.S.U's etc.

Are you carrying out the test between LN-E and are still getting 0.00MegOhms? Can you be sure it is correct neutral mate.
 
I have the line and neutral connected together and testing between that and the earth bar.

The circuit was energised and working fine on arrival (doing an eicr) so it cant be an actual dead short or the mcb would have tripped.

If it's a short between neutral and earth, it won't trip the mcb, but will show up on a 'L+N to E' IR test.
 
If you are getting 0.0 Mohm then try a continuity test to see if you are missing something, if you get a reading in ohm then it is probably something about your testing method.
If there is another circuit crosslinked to this and the main switch is on then you will get 0.0 Mohms.
If you are getting say 0.5 Mohms then you are likely to have a power supply connected.
The other thing to try is test at 250V and see if the result is OK, then it may be a plug in surge protected socket.
 

Reply to IR method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock