Discuss Is it meant to do this? in the Industrial Electricians' Talk area at ElectriciansForums.net

conversation i had with a builder today went something like this...............



you can't put that shower in the bathroom.

why not?

because it's 10.8kw and your cable's only 6 mill' squared.

so what?

so you need a bigger cable or a smaller shower.

why?

because the shower you've got has a FLC of over 45A, and your cable is only rated at 38A.

it'll be alright.

no it won't.

'course it will.

well, why did you ask me then?

because i wanted your advice.

so why are you arguing with me then?

i'm not, you're just wrong. everyone knows a shower's wired in 6mm cable.

see you later.

Nooooob head
 
Crisper, with the greatest respect, if your electrician "mate" is going to connect it all up, test it, fill out the EIC and notify the install to LBC as his work, I would strongly suggest that you take his advice and not a public forums'.
When people come on here asking for advice stating that an electrician will get involved "at the end", it normally means there isn't one.
 
copper???? too expensive. when a 2" nail will do the job just as well.
 
conversation i had with a builder today went something like this...............



you can't put that shower in the bathroom.

why not?

because it's 10.8kw and your cable's only 6 mill' squared.

so what?

so you need a bigger cable or a smaller shower.

why?

because the shower you've got has a FLC of over 45A, and your cable is only rated at 38A.

it'll be alright.

no it won't.

'course it will.

well, why did you ask me then?

because i wanted your advice.

so why are you arguing with me then?

i'm not, you're just wrong. everyone knows a shower's wired in 6mm cable.

see you later.

WOW!!! ............ Talk about Deja Vu - this is almost exactly the same conversation I had last week with my builder mate who I have been trying to help!!

Looks like some folk just can't or won't be helped.
 
I think what we all come across is the fact that builders/plumbers/tilers etc. are all doing electrical work that they shouldn't. When they get a chance to confirm (ask) if what they have been doing is ok, and we say it isn't, they simply get upset and argumentative because they know they're in the wrong but can't do anything about it now.
Sooo many other trades think that it's all easy and straightforward because they've watched a sparky carry out a particular job, they just rush blindly into getting it to work, then job done.
 
get rid of those horrible 3036 fuse boards and replace all 3 with a nice split load, RCD board.

might aswell RCD all circuits if its suitable, much safer than your current setup..
 
get rid of those horrible 3036 fuse boards and replace all 3 with a nice split load, RCD board.

might aswell RCD all circuits if its suitable, much safer than your current setup..

My thoughts exactly. ( >for the pessimists< My imaginary 'sparky' mate, who is not currently overseas dodging bullets for 'Queen and country. And will not be doing the legal stuff when he comes back on R&R has basically said the same. The reason I'm on here is to get an idea of what to 'fix to walls' and 'proper' cabling so when/if he gets back, he doesn't have to fish about doing the 'donkey work'... he deserves a rest after all ;))... Thanks 'shocking_eg' ... appreciate your time.
 

Reply to Is it meant to do this? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
677
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi, I'm new here so apologies if this isn't the correct area to post this. We moved in to a bungalow around 8 months ago and had a full re-wire...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock