I know you are not supposed to do a insulation test on circuits that are protected by an RCD at 500v because it may damage the electronic components inside the RCD so that's why you switch the RCD off before you test the individual circuits, however, what if the circuits are all protected by RCBO's, in this case are the electronic components in the RCBO somehow designed differently so it can be tested at 500v and not get even slightly damaged or do you just do the insulation test at 250v instead?

Thanks.
 
Some RCBO's will let you do insulation testing at the out going terminals, fairly sure the new compact Hager ones do! Best to refer to MI if in any doubt.
Tbh I usually disconnect them for testing.
Sy
 
Some RCBO's will let you do insulation testing at the out going terminals, fairly sure the new compact Hager ones do! Best to refer to MI if in any doubt.
Tbh I usually disconnect them for testing.
Sy
They do and have a note on them to that effect. I still take the conductors out though.
 

Reply to Is it ok to do insulation resistance test on RCBO at 500v? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
649
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
777
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock