Dear Forum....

My kettle connects to the mains via a 3-core 0.75mm^2 flexible cable that is about 75cm long. This was the cable that came with the kettle.

The power rating of the kettle is from 1800-2200 Watts, which means it is drawing between 7.8 and 9.6 amps (using nominal voltage of 230V)

The wiring regs state that a 0.75mm^2 cable has a maximum current carrying capacity of 6 amps.

Then why is the cable supplied not 1.00mm^2 instead...which has max c.c.c. of 10 amps?

Thanks to all.

Wayne :smilewinkgrin:
 
Hello...I thought that c.c.c. could never be exceeded. Also, I thought that cable length only came in to play when considering voltage drop in installations.

So, what you are saying is that because of the load operating for a short time and a short cable length...it isn't really an issue??

Thanks
 
not the only situation where flex on appliances is undersized. i came across a 2kW downflow heater (which can be running for hours at a time) fitted with 0.75mm flex, fed from a 13A FCU. manufacturers instructions stipulated a 13A fuse, so it's a case of us sparks abide by the regs. but these idiots do as they please.
 
Saves the manufacturers a few quid over millions of units. Totally agree tel, we have to follow rules which include safety margins, whereas they take them to the limit.
 
I've noticed this too. Kettle cables often appear to be undersized. I understand that the tabulated cable ratings are largely determined by the rate of degradation of the insulation when run at the rated current for long periods. Due to thermal inertia, cables take a while to reach their maximum temperature when at full load. When used for a kettle, which will only be loaded for a couple of minutes at a time and unlikely to be used more than a few times per hour, the manufacturers can get away with a lower rated cable. Also, modern kettles seem to have a limited lifetime and will probably have failed and been chucked away before the cable insulation degrades too far.
 
even at a full 13a it will still take that .75 flex an hour to warm up
not really a problem for a 2 minute boil kettle.

plus the fact that appliances and factory assembled equipment do not need to follow the CCC guidelines in bs7671 , other standards are followed for product safety compliance
 
You'll probably find the answer to the OP's Q is much simpler: the manufacturers of the kettle will have taken the spec for the cable from it's makers, not from some generic worst case scenario table. If you actually do the full cable calcs yourself and apply every derate component accurately you'll probably find you get a very different answer!!
 

Reply to Is the flexible cable big enough? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello I have a new AEG induction hob rated at 7.4kw max using power sharing but AEG do not specify a cable size or mcb rating nor will they...
Replies
5
Views
2K
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
Replies
8
Views
6K
Specialist
S
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
C
Hi, first time poster here. I've had a relatives iron come my way that is in need of a replacement mains cord but I'm a little confused as to...
Replies
7
Views
1K
M
Hi all, Your help would be appreciated. We are mainly domestic sparx so I havn't much experience with cable sizing for motors. On site, we...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock