Currently reading:
Is this really correct?

Discuss Is this really correct? in the Australia area at ElectriciansForums.net

S

Sparky83

Hi guys,

On a forum i often go on someone was asking about the MEB to there gas pipe as the gas engineer had pointed out that there was bonding to both side of the gas meter.

Someone asked this question...

Aren't gas mains plastic too? What is the earthing for, to protect those inside the property from an issue that causes the pipework to become live?


Somebody whom says they are an electrician said the following...

its to stop external influences affecting your metal work essentially, nowadays most incoming gas/water bonds are plastic and don't need the equipotential bonding to them but most sparkies do it anyway, just disconnect the before clamp wire and put it in the post clamp terminal, easy job and should take 2 mins. nothing will happen when you remove it, just make sure its tight enough not to pull out and the clamp should not spin on the pipe either

Now is this correct? As im pretty sure that you always need the MEB to be in place?

I did question this with him and his reply about did he mean supps was...

main bonds too, i know it seems crazy to me too, it come up on my last nic inspection i went to.

he asked why i bonded main earth and water when they was plastic incoming. if its not metal incoming into the property the the metal work is inside is classed as supplementary, (not required now) he then proceeded to ask me how i would get a shock from metal work if it wasn't even connected to the "installation" with so many instances where continuity cannot be obtained on all pipe work then there should never be a potential difference between materials. hence no bonds no difference. obviously all circuits in said install have to be 30ma rcd protected
xyxthumbs.gif


(again im no lecturer but those who have niceic inspections know how ---- they can be, so only going on what im told)

Hope it makes sense, Any thoughts on the above?
 
Some older properties had (still have) the gas and/or water pipe as the main earth. As these supply pipes are being converted to plastic they are failing to provide earthing to the property.

PJ
 
Because of incoming plastic service supplies - the need for equipotential Bonding is a must, this is because the metal pipework within the installation is effectively isolated from ground. If no bonding was present then a fault Live - earth (gas/water pipes) would create a 230v potential between all the metal pipework, sinks etc etc and anything connected to earth like appliances the floor itself thus been in contact with both item would see you become part of the fault circuit EEEK!.
Before plastic incoming pipes they were brought in in lead,steel, iron etc etc which because its conductive and was buried in the ground gave natural earth bonding, this is why older installation may have no bonding at all, and in some cases earthing was pinched off the pipework if needed for a light etc.
The muppet on said other site is a dangerous mouth and if you could just PM him and send him to this site maybe he may learn a thing or 2 before he puts someone in danger.
 
Its the first time I have had a look at my new green onsite guide. However, pages 40,41,42 seem to verify what you were saying about not installing main bond to plastic incoming services. The HOWEVER is that you have to confirm that any metallic pipework within the building is not introducing earth potential.
 
Because of incoming plastic service supplies - the need for equipotential Bonding is a must, this is because the metal pipework within the installation is effectively isolated from ground. If no bonding was present then a fault Live - earth (gas/water pipes) would create a 230v potential between all the metal pipework, sinks etc etc and anything connected to earth like appliances the floor itself thus been in contact with both item would see you become part of the fault circuit EEEK!.
Before plastic incoming pipes they were brought in in lead,steel, iron etc etc which because its conductive and was buried in the ground gave natural earth bonding, this is why older installation may have no bonding at all, and in some cases earthing was pinched off the pipework if needed for a light etc.
The muppet on said other site is a dangerous mouth and if you could just PM him and send him to this site maybe he may learn a thing or 2 before he puts someone in danger.

Really DW?

I would say that if your start bonding metal work that wasn't an extraneous conductive part then you more likely to make that piece of metal live during a fault. We after all don't bond metal door frames, windows etc, as they have no contact with earth, and so bonding a metal pipe within an installation, that as no connection with earth, ie main pipe coming in plastic, but internal installation is copper, is IMO not needed.

Of course it is always best to check if the pipe is an extraneous conductive part, but if it isn't it don't need bonding
 
Hi guys,

On a forum i often go on someone was asking about the MEB to there gas pipe as the gas engineer had pointed out that there was bonding to both side of the gas meter.

Someone asked this question...

Aren't gas mains plastic too? What is the earthing for, to protect those inside the property from an issue that causes the pipework to become live?


Somebody whom says they are an electrician said the following...

its to stop external influences affecting your metal work essentially, nowadays most incoming gas/water bonds are plastic and don't need the equipotential bonding to them but most sparkies do it anyway, just disconnect the before clamp wire and put it in the post clamp terminal, easy job and should take 2 mins. nothing will happen when you remove it, just make sure its tight enough not to pull out and the clamp should not spin on the pipe either

Now is this correct? As im pretty sure that you always need the MEB to be in place?

I did question this with him and his reply about did he mean supps was...

main bonds too, i know it seems crazy to me too, it come up on my last nic inspection i went to.

he asked why i bonded main earth and water when they was plastic incoming. if its not metal incoming into the property the the metal work is inside is classed as supplementary, (not required now) he then proceeded to ask me how i would get a shock from metal work if it wasn't even connected to the "installation" with so many instances where continuity cannot be obtained on all pipe work then there should never be a potential difference between materials. hence no bonds no difference. obviously all circuits in said install have to be 30ma rcd protected
xyxthumbs.gif


(again im no lecturer but those who have niceic inspections know how ---- they can be, so only going on what im told)

Hope it makes sense,Any thoughts on the above?
Hi
sparky83

Wrt the mention of supp bonding not required now, this tends to be a blanket statement and is not nec. True. It depends. Not every circuit in a house, even under the 17th, amended, HAS to be on an RCD. This another blanket belief. In fact I have a socket in my garage that has no RCD PROTECTION!
 
There is always conflict of opinion on the forum for necessity for main bonding

I posted a link in another tread to an article by Paul Cook of the Iet
It is worth reading because its a simple outline of why and what requires to be bonded,given the various combinations of internal and supply service materials

Please note the following,quoted from the article

It is important to note that the reference above is always to metal pipes. If the pipes
are made of plastic, they do not need to be main bonded.

If the incoming pipes are made of plastic, but the pipes within the electrical
installation are made of metal, the main bonding must be carried out

In the link there is also a chart that details combinations of materials in a bathroom where supplementary bonding can be assessed

Here is that link
http://www.plasticpipesgroup.com/pdfs/earthbonding.pdf
 
There is always conflict of opinion on the forum for necessity for main bonding

I posted a link in another tread to an article by Paul Cook of the Iet
It is worth reading because its a simple outline of why and what requires to be bonded,given the various combinations of internal and supply service materials

Please note the following,quoted from the article

It is important to note that the reference above is always to metal pipes. If the pipes
are made of plastic, they do not need to be main bonded.

If the incoming pipes are made of plastic, but the pipes within the electrical
installation are made of metal, the main bonding must be carried out

In the link there is also a chart that details combinations of materials in a bathroom where supplementary bonding can be assessed

Here is that link
http://www.plasticpipesgroup.com/pdfs/earthbonding.pdf

Thanks for the replies guys, i understand not bonding the plastic pipes, but thought you would need to bond them where the plastic meets the metal pipe, and having read the link above it would seem this is the case.

Thanks again.
 
What a wonderful thing our industry is there is someone. Paul Cook regarded as an authority claiming that if incoming is plastic but installation is metal .........off we go and bond away, regardless of whether that metal is an extraneous conductive part

or in our OSG guide section 4.5 we have

"Where there is a plastic incoming service and a metal installation within the premises, main bonding is recommended"

So it would seem My Cook is right, ahhhhhhhhhhhh hold on though , OSG continues

"​unless it has been confirmed that any metallic pipework within the building is not introducing earth potential (see4.3)"


So what do we do, bond away anything that is metal or a pipe in case it introduces a potential, or do our jobs. If I found plastic incoming services gas/water, but metal pipework in the installation, before I start bonding everything in sight I might, just might check to see if that metalwork is in fact an extraneous conductive part.
 
I would also agree with your last post Malcolm
icon14.png


But for many, new to absorbing the straight and narrow unclouded guidlines that are found in our industry :blush5: it is a daunting task to come to a decision themselves, when reliance on those guidlines is so crucial to them,especially when confronted with perhaps an assessor who may have regimented thoughts on the matter and an unbending opinion on what should or should not be done
icon7.png
 
The only reason for main bonding is to tie services introducing an external earth potential to the electrical earthing system....
The only reason for supplementary bonding is to tie services introducing an earth potential into a special location (as defined in bs7671) to the electrical earthing within that location.
Thats all you need to know....not brain surgery....so why do so many fail to get it?
 
Totally agree Des, but if we start bonding bits of metal that don't need it, surely we are in danger of making that piece of metal "live" during a fault.

Ok it will be for milli-seconds if the protection device is correct, and what are the chances during those milli-seconds the wife is touching a bonded non extraneous part, soaking wet, believe me Des I've tried to get all those in place, but she won't stand still long enough.

But still I can't see how bonding a non extraneous part, is making the installation safer.
 
The only reason for main bonding is to tie services introducing an external earth potential to the electrical earthing system....
The only reason for supplementary bonding is to tie services introducing an earth potential into a special location (as defined in bs7671) to the electrical earthing within that location.
Thats all you need to know....not brain surgery....so why do so many fail to get it?

Address to Mr Cook care of the IE..................................
 
Really DW?

I would say that if your start bonding metal work that wasn't an extraneous conductive part then you more likely to make that piece of metal live during a fault. We after all don't bond metal door frames, windows etc, as they have no contact with earth, and so bonding a metal pipe within an installation, that as no connection with earth, ie main pipe coming in plastic, but internal installation is copper, is IMO not needed.

Of course it is always best to check if the pipe is an extraneous conductive part, but if it isn't it don't need bonding
As mentioned in other post page 42 green OSG states 'where there is plastic incoming service and a metal installation within the premises main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing earth potential.

This is one of those regs that can be misread in my mind, as a golden rule always bond Gas/Water regardless of incoming pipe unless internal pipework is also plastic, consider a live wire under the floor touches a water pipe which has no bonding and has incoming plastic supply... there will then be a floating PD of 230v from say your tap and a adjacent cooker's metal work, its no rocket science to work out the consequences of this situation as ive been called out to exactly this issue, with regards to doors and windows in metal... their was alot of confusion many years ago regarding said bonding and at one point it was necessary but this was soon shelved as the likelyhood of windows and doors becoming live and a risk to safety was neglegible as well as been screws/bolted to the building mass too which would give a easier earth path than joe bloggs opening door.
Yes agree circumstances do exist where you dont need to bond gas/water if incoming plastic and metal internal but it would require thorough checking that it dosnt introduce earth potential and is prone to other trades altering their installs and making bonding a requirement.... so to sum up i reckon its best to do it regardless of incoming pipe.
 
Last edited:
But still I can't see how bonding a non extraneous part, is making the installation safer.

The only reason I can think of why they give this advise and it still makes no justification for doing so
icon4.png
,is,is,is,is and I have just thought about it,and even my thoughts come to a full stop
icon11.png


So my conclusion must be,minds better able than my own have made this assessment and who am I,but a wilting spark to be so bold and argue the point
icon6.png




believe me Des I've tried to get all those in place, but she won't stand still long enough.
Come now,there are less brutal ways of divorcing the dear one
icon12.png
 
Last edited:
As mentioned in other post page 42 green OSG states 'where there is plastic incoming service and a metal installation within the premises main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing earth potential.

This is one of those regs that can be misread in my mind, as a golden rule always bond Gas/Water regardless of incoming pipe unless internal pipework is also plastic, consider a live wire under the floor touches a water pipe which has no bonding and has incoming plastic supply... there will then be a floating PD of 230v from say your tap and a adjacent cooker's metal work, its no rocket science to work out the consequences of this situation as ive been called out to exactly this issue, with regards to doors and windows in metal... their was alot of confusion many years ago regarding said bonding and at one point it was necessary but this was soon shelved as the likelyhood of windows and doors becoming live and a risk to safety was neglegible as well as been screws/bolted to the building mass too which would give a easier earth path than joe bloggs opening door.
Yes agree circumstances do exist where you dont need to bond gas/water if incoming plastic and metal internal but it would require thorough checking that it dosnt introduce earth potential and is prone to other trades altering their installs and making bonding a requirement.... so to sum up i reckon its best to do it regardless of incoming pipe.

I can see you getting slated for that comment by some here....lol!!
 
As mentioned in other post page 42 green OSG states 'where there is plastic incoming service and a metal installation within the premises main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing earth potential.

This is one of those regs that can be misread in my mind, as a golden rule always bond Gas/Water regardless of incoming pipe unless internal pipework is also plastic, consider a live wire under the floor touches a water pipe which has no bonding and has incoming plastic supply... there will then be a floating PD of 230v from say your tap and a adjacent cooker's metal work, its no rocket science to work out the consequences of this situation as ive been called out to exactly this issue, with regards to doors and windows in metal... their was alot of confusion many years ago regarding said bonding and at one point it was necessary but this was soon shelved as the likelyhood of windows and doors becoming live and a risk to safety was neglegible as well as been screws/bolted to the building mass too which would give a easier earth path than joe bloggs opening door.
Yes agree circumstances do exist where you dont need to bond gas/water if incoming plastic and metal internal but it would require thorough checking that it dosnt introduce earth potential and is prone to other trades altering their installs and making bonding a requirement.... so to sum up i reckon its best to do it regardless of incoming pipe.

This is confusing bonding with earthing...the two are entirely different. If it was necessary to earth all metallic pipe within an equipotential zone the regulations would require a test of pipework to ensure continuity from the nearest to the furthest point in the building. No such test is required....If your purpose in bonding is also to earth metallic pipework,then clearly you have failed if you do not verify a low continuity through the entire system.
 
Last edited by a moderator:
I can see you getting slated for that comment by some here....lol!!

At 40 im may be old Hat but we were taught its required to be done with the exception of all plastic pipe incoming and internal, ive witness circumstances where bonding hadn't been done and resulted in shock, even on incoming plastic, i believe all the regs and guidelines have done here is to show you there does exist circumstances when it wouldnt be necessary when incoming plastic and internal metal piping but they also cover it with a recommendation to be done, this will avoid others trades making alterations and leaving the pipework needing bonding where as it didnt require it before. I believe they have included this exclusion as circumstances can exist where its not needed but more for your knowledge rather than for you to not bother doing it, regulations are changed and ammended all the time and its probably because select ppl made this point that situation can exist where not needed so they had to include it rather than leave it out.

Im good for debate and im also happy to stand corrected and admit it but i enjoy banter and different views it throws up... with all respect i learnt indepth on the 15th edition and 20 yrs just keeping up with changes but without healthy debate ppl can become stubborn and set in there ways whether they are right or wrong.
 
DW what if we have a nail that goes exactly through a LINE conductor, but does not damage or touch the NEUTRAL/EARTH conductors ................ There is just a good a chance that will become live as your pipe.

To me it is risk assessment, IMO there is more of a danger that you make the installation less safe by bonding metal work that are non extraneous conductive parts, that the scenarios we have mentioned.

I totally agree there is more danger in yours, than mine and a damaged cable under a floor in the bathroom can touch a pipe there and transfer down to a sink with someone touching across it, but there is also the danger of under a fault condition that pipe become live because you bonded it.

For me it is just the blanket if it plastic incoming, metal inside .....bond it .............regardless of what it is. I just think it takes the not thinking for ourselves away from us
 
DW what if we have a nail that goes exactly through a LINE conductor, but does not damage or touch the NEUTRAL/EARTH conductors ................ There is just a good a chance that will become live as your pipe.

To me it is risk assessment, IMO there is more of a danger that you make the installation less safe by bonding metal work that are non extraneous conductive parts, that the scenarios we have mentioned.

I totally agree there is more danger in yours, than mine and a damaged cable under a floor in the bathroom can touch a pipe there and transfer down to a sink with someone touching across it, but there is also the danger of under a fault condition that pipe become live because you bonded it.

For me it is just the blanket if it plastic incoming, metal inside .....bond it .............regardless of what it is. I just think it takes the not thinking for ourselves away from us

I agree it is risk asses' but not knowing your age here, i can remember niceic telling us to bond ceiling grid work, then following year not required, same with sinks etc ive seen some of these circumstances repeat more than once and at the time were regs, its seems to be less strict now but i can only assume the mass introduction of RCD on most circuits now means bonding is not the bees knees it once was and can be relaxed under certain circumstances. Im probably more set in my ways through experience where ive seen lack of such bonding result in someone getting nasty shock, now times are a changing and an RCD would have minimised said shock had it been reg's in them days.
 
Well mate i'm a bit older than you ............:arabia: .....................not as old as Tel though.

If you take my house the incomer is plastic to the SC. Then copper into the downstairs Bathroom, but then tee of into the sink and shower with plastic.

The copper goes on to kitchen where it was completely rerouted because we moved the boiler. It tees off into the kitchen in plastic but then carries on to the outhouses in copper.............so I could bond the that pipe.

We plastic up to the boiler upstairs. In kitchen though the pipework going upstairs is copper to the bathroom and the en-suites, we fed the riser from the plastic pipe, Now the en-suite is not been touched pipe wise so it's all copper, but the bathroom is tee off in plastic from the riser, and does the bath, shower handbasin etc. so plastic ok.

But unfortunately 2 bedrooms have vanity sinks and all these are still in copper that are teed of that plastic bathroom pipe ......................at this rate I would have BS 951 clamps everywhere.

I don't have main bonding because it is plastic incomer, and I IR every pipework in the outhouse and the bathrooms and none are extraneous conductive parts
 
Well mate i'm a bit older than you ............:arabia: .....................not as old as Tel though.

If you take my house the incomer is plastic to the SC. Then copper into the downstairs Bathroom, but then tee of into the sink and shower with plastic.

The copper goes on to kitchen where it was completely rerouted because we moved the boiler. It tees off into the kitchen in plastic but then carries on to the outhouses in copper.............so I could bond the that pipe.

We plastic up to the boiler upstairs. In kitchen though the pipework going upstairs is copper to the bathroom and the en-suites, we fed the riser from the plastic pipe, Now the en-suite is not been touched pipe wise so it's all copper, but the bathroom is tee off in plastic from the riser, and does the bath, shower handbasin etc. so plastic ok.

But unfortunately 2 bedrooms have vanity sinks and all these are still in copper that are teed of that plastic bathroom pipe ......................at this rate I would have BS 951 clamps everywhere.

I don't have main bonding because it is plastic incomer, and I IR every pipework in the outhouse and the bathrooms and none are extraneous conductive parts

Does it make any difference that all this pipework is linked by conductive water, so even if a live cable was to touch a metal pipe would it not effect someone touching the pipework that is the other end of a bit of plastic pipe?? If that makes sense???
 
Does it make any difference that all this pipework is linked by conductive water, so even if a live cable was to touch a metal pipe would it not effect someone touching the pipework that is the other end of a bit of plastic pipe?? If that makes sense???

I seem to remember reading of an experiment by Chris Kitching in his Inspection & Testing book in which he proved that water is not such a good conductor of electricity as some of us think it is.

The section in the book is the one about bonding plastic pipes ........ or not.
 
I have to say I dont get the fixation with pipes being live,or becoming live....it just doesnt happen. Most of the copper sections of pipework will be earthed anyway by means of being in contact with conductive parts such as M/V's....immersion heaters....boilers etc. Often those who claim to be getting shocks off live pipes are mistaken anyway. Example.....I got called out to a property where a plumber was changing a boiler and claimed all the pipes were live,he refused to carry on until it was sorted. What in fact had happened was he had caused a bit of a flood draining down,and in an adjacent larder a cable dropped through a hole in the floor,this cable had been chewed by rodents and the live core was exposed. Water had reached the cable and plumber boy was kneeling in it,every time he touched a pipe,which was earthed,he got a shock via the water on the floor. Of course he assumed the pipes were live.
 
Last edited by a moderator:
Just a note on the conductivity of water. I worked on a 1200V system that could be loaded up to 4000A. To keep the flexible conductors cool water was pumped though them. There was very close monitoring of earth leakage that would trip at 50mA. It never gave a problem.
 

Reply to Is this really correct? in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock