Discuss Isolate circuit but trips fuse board in the UK Electrical Forum area at ElectriciansForums.net

Ellsa100

DIY
Reaction score
5
Hi

Weird problem.

I’m replacing plug sockets. I isolate the circuit for the particular sockets at the fuse board so it is safe to swap out. All good. Suddenly the RCCB for all sockets - not just the circuit of the sockets I have isolated - trips. Why is this happening?

The RCCB doesn’t trip when all the circuits are live. It is as if it won’t let me isolate an individual circuit as it trips the whole consumer unit shortly after I isolate a circuit

Thanks
 
If by “isolate the circuit” you mean that you turned off the MCB then you have not isolated the circuit fully. The MCB only turn off the line.
To fully isolate a circuit you need to disconnect the neutral as well.

The RCBO/RCD may trip if the neutral is still connected and you touch a neutral conductor to earth.
 
If by “isolate the circuit” you mean that you turned off the MCB then you have not isolated the circuit fully. The MCB only turn off the line.
To fully isolate a circuit you need to disconnect the neutral as well.

The RCBO/RCD may trip if the neutral is still connected and you touch a neutral conductor to earth.
Oh maybe that is it - I flicked the MCB - so you are saying that an earth and the neutral touched? Thanks
 
How do I disconnect the neutral after turning off the MCB?
It would be dangerous to try unless you've had plenty of practise. Please don't try and do this.

Just change the sockets under daylight hours, isolate the circuit as you did (or better just use the main switch), and try and avoid touching the wires together. When changing sockets it shouldn't be too hard to keep them separate.

The reason is that the Neutral wire is connected to other Neutral wires and touching it to earth is providing an alternative path back for some current, so the safety device kicks in just in case this current is going through a person.
 

Reply to Isolate circuit but trips fuse board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
786
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
818
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock