Discuss Isolation for a bathroom fan in the Commercial Electrical Advice area at ElectriciansForums.net

M

Mark payne

Hello I work as a maintenance man in a hotel that has recently been fitted with Greenwood Unity CV2GIP bathroom fans. These fans run constantly, full speed when the light is on and trickle speed when the light is off.
No isolation switch has been fitted for these fans other than turning off the MCB in the small fuse board in the bedroom.
Does this comply with the current wiring regulations? I thought that a triple pole isolater should have been fitted, but not sure if it is a regulation or recommendation.
If anyone could enlighten me and possibly give me the regulation number it would be a great help.
 
thw whole purpose of a fan isolator is to enable you to isolate the fan without killing the lights, in order to be able to see when servicing/replacing fan, so in this case, a fan isolator is desirable.
 
Hi,i suppose full isolation can be achieved from the DB,which will not be a million miles from where a 3 pole would be...

That,and the fact that fitting a separate isolator could be 2/3's more work:)
 
As far as I am aware there is no specific regulation for extractor fans isolation.
Regulation 537.2.1.2 specifies that suitable means must be available to prevent inadvertent energisation.
However this can be provided in a domestic situation by the MCB or the main switch.
The electricians guide to the building regulations states that for fans in bathrooms without a window that a fan should be (not must be) provided with a triple pole isolator so that changing the fan can be done with the light on.
However any other item of electrical equipment on a lighting circuit would have to be changed in the dark as a matter of course so this seems a little OTT.
In general the accepted practice is to provide a triple pole isolator as it avoids later questions about safety, but I do not believe it is a specific requirement.
In your case there is a means of isolation available and you would not want guests to switch off a local isolator for a continuous extract system.

and I am typing way too slowly as three posts have come in since I started typing!
 
As far as I am aware there is no specific regulation for extractor fans isolation.
Regulation 537.2.1.2 specifies that suitable means must be available to prevent inadvertent energisation.
However this can be provided in a domestic situation by the MCB or the main switch.
The electricians guide to the building regulations states that for fans in bathrooms without a window that a fan should be (not must be) provided with a triple pole isolator so that changing the fan can be done with the light on.
However any other item of electrical equipment on a lighting circuit would have to be changed in the dark as a matter of course so this seems a little OTT.
In general the accepted practice is to provide a triple pole isolator as it avoids later questions about safety, but I do not believe it is a specific requirement.
In your case there is a means of isolation available and you would not want guests to switch off a local isolator for a continuous extract system.

and I am typing way too slowly as three posts have come in since I started typing!
 
Yep,it's a post-race!...
I cannot remember seeing many isolators fitted,in the hotels i have visited,i think this is to save patrons who do not like the noise of a fan,to leave a clammy bathroom,for the next person.

Anyway,i'm sure we all stay in hotels that are so luxurious,that their bathrooms contain large,feature windows,to allow working on the fan,in daylight hours (which is the only time they fail;))
 
Yep,it's a post-race!...
I cannot remember seeing many isolators fitted,in the hotels i have visited,i think this is to save patrons who do not like the noise of a fan,to leave a clammy bathroom,for the next person.

Anyway,i'm sure we all stay in hotels that are so luxurious,that their bathrooms contain large,feature windows,to allow working on the fan,in daylight hours (which is the only time they fail;))
 
I'd get a hold of the installation instructions for said fan and see what the manufacturers require. The regs require manufacturers instructions to be taken into account, so if they ask for an isolator I'd be inclined to fit one just to make sure I'm not on the wrong side of the regs.
 
The problem I have is that there two fans stuck on full speed that won't reset and the contractor won't be back to fix them for a week or so. I can't disconnect them as it is a windowless bathroom, so an isolactor just for the fan would have been useful
 
I'd get a hold of the installation instructions for said fan and see what the manufacturers require. The regs require manufacturers instructions to be taken into account, so if they ask for an isolator I'd be inclined to fit one just to make sure I'm not on the wrong side of the regs.
 
Regulation 134.1.1 on page 21 of the big yellow book states:-

"Good workmanship by skilled or instructed persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers' instructions."
 
Mark, the issue with the regs is that it's not a statutory document. The advice from a sparks point of view is that if you follow the regs, evidence that you have done so presents a strong case in your defence if something goes wrong. It could be they elected not to fit them, but my understanding is that would need to be recorded as a departure from BS7671 (the regs) and should have included a risk assessment so that whoever made that decision can demonstrate they thought about the situation upfront and concluded that in that given scenario it's acceptable to not fit the isolator.

The fact the lights go out isn't a problem from a sparks perspective, it's our normal working environment, but if used in a domestic setting, the householder may not be equipped to deal with it so it's preferential to keep the lights on which requires the isolator so they can work on the fan.
 
Because the manufacturers instructions state the fan must have a triple pole isolator then one should have been provided (probably in a location to which guests do not have access.

In your current position, as you have described, I would switch off the lighting MCB and disconnect the power supply to the fan and terminate safely (if this is within your skill set) and then restore the power to the lighting circuit.
 
Thank you everyone who replied to my question. The area manager is calling to see me on Thursday to look at the problem. When he spoke to the installation contractor they claimed that they didn't need to fit an isolator as they were connecting the new fan to the existing wiring (which was probably 15th edition installation) this isn't true as all the wiring on each floor was ripped out during the refurbishment.
I will let you know what the outcome is.
 

Reply to Isolation for a bathroom fan in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
661
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Looking for counsel / guidance to replace an original Dayton On/off with speed control switch. I’ve checked with a couple local electrical supply...
Replies
5
Views
675
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
613
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock