Discuss Isolator for ryefield board. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello,

I’m about to take on a mains room for a block of flats and the DNO are giving us a supply of 259kva.

Now, would I need a 200amp TP-N isolator or a 400amp TP-N isolator from the main head to the ryefield board? I am also assuming I will require a CT chamber. This is my first project of this kind. Any advice would be appreciated.
 
sounds like a 400A supply to me.

this is a complicated setup, and it is important to figure out who is doing what.

if the building operator is buying electricity and then sub metering to the flats, you probably don't need a ct chamber, as it will be installed by the supplier when they put the meter in.

if their are to be multiple connections and meters off the same incoming supply, you need to discuss with the DNO who has the responsibility for the distribution between incomer and meters, it is not always down to the DNO in this sort of application.
 
sounds like a 400A supply to me.

this is a complicated setup, and it is important to figure out who is doing what.

if the building operator is buying electricity and then sub metering to the flats, you probably don't need a ct chamber, as it will be installed by the supplier when they put the meter in.

if their are to be multiple connections and meters off the same incoming supply, you need to discuss with the DNO who has the responsibility for the distribution between incomer and meters, it is not always down to the DNO in this sort of application.
Nice one. Thanks James.
 

Reply to Isolator for ryefield board. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am currently in the process of quoting a job to renew the mains for 19 flats. This is the first job of this type that I have quoted so...
Replies
2
Views
739
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
728
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
952
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock