Had a call today saying upstairs lights not working, tripped yesterday but now nothing working. Thought it would probably be something simple, but oh no!

No supply to any ceiling roses, not a thing anywhere! MCB makes and breaks ok. Copper making contact in the MCB OK.

Couldn't stay long so said I'll be back tomorrow morning.

Got to be an issue with the supply cable going up into the loft, trouble is I don't know which ceiling rose it connects to first or the route of the cable.

Just trying to get a 'plan of attack', probably have to use a flying lead!

Any other good ideas?
 
get in attic with voltstick once you have determined that it's not a lost N.
 
Is the hall light working? the upstairs lights may be fed from the hall!

Start with the light closest to the supply point of entry to the loft and use a cable tracer back toward the CU until it stops signalling, there is the break.
 
I had similar recently when installing some new extractors. It was a convoluted set up I did which meant several hours of knocking about in the loft. Long story short, the vibrations from constantly banging about dislodged a really poor neutral connection at a light fitting. Didn't take long to find it once I was in the loft, <45 mins. This dodgy connection knocked out three other light fittings and resulted in something like 100V only getting through to the fan.

If I was you I would try voltstick first to see if anything quickly shows up. If no joy, then bell it out with a wander lead.

Have the occupiers done anything recently that may have caused it. Sometimes you have to tease info out of them!
 
I got called to a property where the bathroom light had just stopped working. Been there before, when lady run over hoover lead. Sure enough light/extract fan not working. Took down surface spot, no power. Went to landing and hey, is that a new ceiling rose? Oh yes says the lady, had a nice man here from 'Fifty Plus' (something like that), who did some painting for me. He put up a light fitting in the lounge & changed some old ceiling roses. Loose connections in ceiling rose, and new metal light fitting in lounge not earthed! Next time I'll ask first, 'Have you had anyone else here?'.
 
Last edited:
Update on the story!

Went back this morning, straight up in the loft with my voltstick, nothing anywhere. Followed the cables around and found the first port of call when exitting the conduit up the wall. Pulled the CU apart to get the cable out straight to see if there is any damage there! Long lead test on the cable - L-open, N-good, E-open! Also L-N shorted at light fitting end.

Scratching my head by now, and then the owner tells me she had a handrail put up on the stairs earlier in the week! Yes, I did ask earlier if anything had been done, but she is in her 90s, bless her! I knew the cable feed was going up the wall in the area, not in a safe zone though, and it looks like the guy hit the cable!

So had to run another feed and all is well!
 
Update on the story!

Went back this morning, straight up in the loft with my voltstick, nothing anywhere. Followed the cables around and found the first port of call when exitting the conduit up the wall. Pulled the CU apart to get the cable out straight to see if there is any damage there! Long lead test on the cable - L-open, N-good, E-open! Also L-N shorted at light fitting end.

Scratching my head by now, and then the owner tells me she had a handrail put up on the stairs earlier in the week! Yes, I did ask earlier if anything had been done, but she is in her 90s, bless her! I knew the cable feed was going up the wall in the area, not in a safe zone though, and it looks like the guy hit the cable!

So had to run another feed and all is well!

Did you manage to pull through the conduit.? Suppose not with an screw through it.
 
Last edited:
Did you manage to pull through the conduit.? Suppose not with an screw through it.


Didn't really want to route the old way because it wasn't in a safe zone and thats what happens when cables are not in safe zones!

Managed to route cable with some other cables on the surface under the stairs and then used my supperrods to get under the floorboards to the airing cupboard (where there was a loose floorboard), and up inside the airing cupboard!
 
Didn't really want to route the old way because it wasn't in a safe zone and thats what happens when cables are not in safe zones!

Managed to route cable with some other cables on the surface under the stairs and then used my supperrods to get under the floorboards to the airing cupboard (where there was a loose floorboard), and up inside the airing cupboard!


yeah, airing cupboards do save the day, not many left most get knocked out. lol
 
Bloody hell! How high was the handrail or how low were the switches! :wink_smile:

EDIT: just re read and realised it wasn't a switch drop.... Doh!! And even if it was it wouldn't cause the symptoms...
 
Last edited:
Update on the story!
Scratching my head by now, and then the owner tells me she had a handrail put up on the stairs earlier in the week! Yes, I did ask earlier if anything had been done, but she is in her 90s, bless her! I knew the cable feed was going up the wall in the area, not in a safe zone though, and it looks like the guy hit the cable!
Yep I was always taught to expect the unexpected and ask them to state the bleeding obvious, except I've seen to forget my own advise!
 

Reply to Job for tomorrow in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
884
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
647
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
528
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
743
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock