I'm not familiar with the UK rules on maintenance free connections but couldn't you use a small resin joint?
 
Buried in the wall, no. Requires a complete assembly complying with BS5733 MF which will incorporate strain relief etc. Note that most insulated crimps are not suitable for solid conductors.
 

Attachments

  • Screenshot_20230524_122134_DuckDuckGo.jpg
    168.5 KB · Views: 18
Buried in the wall, no. Requires a complete assembly complying with BS5733 MF which will incorporate strain relief etc. Note that most insulated crimps are not suitable for solid conductors.
Is it that it's not suitable or that the standards do not mention solid conductors?
Final throw of the dice - show them D-Line semi-circular trunking. It is much nicer on the eye. I even skimmed over and lightly sanded it once to make it look like it was part of the original plaster cornice in a national trust property.

View attachment 108373
Is that a photo? It looks great if it is. I use the oval stuff quite a bit where people want extra sockets in decorated rooms. I have been quite lucky with getting the cable between dabs and just using the trunking horizontally.
 
Is it that it's not suitable or that the standards do not mention solid conductors?
I know more than I want to about this following an argument with a CPS.

BS5733 MF has a list of 10 tests for an assembly to be suitable for MF joints.
A crimp wouldn't comply, nor would any single connection device be it a wago, ideal connector, choc bloc, etc. as the standard includes strain relief for the cable, needing a tool to open, being marked MF and a load of other stuff.
That is why I say above that an ideal connector cannot possibly comply on it's own.

Wago, and now Ideal have jumped through all the hoops and their enclosures and connectors together comply with BS5733 MG if you follow their precise instructions.

Stop reading now if you don't like sarcasm.

Previously Wago boxes and connectors only met the standards below so obviously this was totally inadequate:
Mechanical Tests.

* Pull-Out Test to IEC/EN 60947-7-1, IEC/EN 60998-2-2, IEC/EN 60999-1

* Shock Test to IEC/EN 60068-2-27, 60068-2-30; Railway Applications IEC/EN 61373

* Vibration Test to IEC/EN 60068-2-6; Shipbuilding GL, LR, DNV; Railway Applications EN 61373

Electrical Tests

* Temperature-Rise Test to IEC/EN 60947-7-1, IEC/EN 60998-1, IEC/EN 1-61984

* Derating Curve to IEC/EN 60512-5-2

* Voltage Drop Test to IEC/EN 60947-7-1

* Short-Time Withstand Current Test (Short-Circuit Withstand Capacity) to IEC/EN 60947-7-1

* Insulation Parameters to IEC/EN 60664-1

* Power-Frequency Withstand Voltage Test to IEC/EN 60998-1

* Rated Impulse Withstand Voltage Test to IEC/EN 60664-1

* IP Ratings for Electrical Equipment to IEC/EN 60529

Material Tests

* Needle Flame Test to IEC/EN 60695-2-2

* Glow-Wire Test to IEC/EN 60998-1, IEC/EN 60695-2-11

Environmental Tests

* Temperature Cycling Test to IEC/EN 60947-7-1, IEC/EN 60998-2-2

* Industrial Atmospheres to EN ISO 6988, IEC 60068-2-42, IEC/EN 60068-2-60

* Salt Spray Test to IEC/EN 60068-2-11, Marine Applications GL, LR, DNV

* Quick Change of Temperature to IEC/EN 60068-2-14


You'll be glad to know that they have now passed the newer 10 point test so we can use them after all.
 
I know more than I want to about this following an argument with a CPS.

BS5733 MF has a list of 10 tests for an assembly to be suitable for MF joints.
A crimp wouldn't comply, nor would any single connection device be it a wago, ideal connector, choc bloc, etc. as the standard includes strain relief for the cable, needing a tool to open, being marked MF and a load of other stuff.
That is why I say above that an ideal connector cannot possibly comply on it's own.

Wago, and now Ideal have jumped through all the hoops and their enclosures and connectors together comply with BS5733 MG if you follow their precise instructions.

Stop reading now if you don't like sarcasm.

Previously Wago boxes and connectors only met the standards below so obviously this was totally inadequate:
Mechanical Tests.

* Pull-Out Test to IEC/EN 60947-7-1, IEC/EN 60998-2-2, IEC/EN 60999-1

* Shock Test to IEC/EN 60068-2-27, 60068-2-30; Railway Applications IEC/EN 61373

* Vibration Test to IEC/EN 60068-2-6; Shipbuilding GL, LR, DNV; Railway Applications EN 61373

Electrical Tests

* Temperature-Rise Test to IEC/EN 60947-7-1, IEC/EN 60998-1, IEC/EN 1-61984

* Derating Curve to IEC/EN 60512-5-2

* Voltage Drop Test to IEC/EN 60947-7-1

* Short-Time Withstand Current Test (Short-Circuit Withstand Capacity) to IEC/EN 60947-7-1

* Insulation Parameters to IEC/EN 60664-1

* Power-Frequency Withstand Voltage Test to IEC/EN 60998-1

* Rated Impulse Withstand Voltage Test to IEC/EN 60664-1

* IP Ratings for Electrical Equipment to IEC/EN 60529

Material Tests

* Needle Flame Test to IEC/EN 60695-2-2

* Glow-Wire Test to IEC/EN 60998-1, IEC/EN 60695-2-11

Environmental Tests

* Temperature Cycling Test to IEC/EN 60947-7-1, IEC/EN 60998-2-2

* Industrial Atmospheres to EN ISO 6988, IEC 60068-2-42, IEC/EN 60068-2-60

* Salt Spray Test to IEC/EN 60068-2-11, Marine Applications GL, LR, DNV

* Quick Change of Temperature to IEC/EN 60068-2-14


You'll be glad to know that they have now passed the newer 10 point test so we can use them after all.
And how is a crimp or solder connection any less likely to be pulled apart whilst plastered in than a socket? A lot of this BS is trying to do the thinking for people and make money from it. I believe the wago boxes need to be installed in free air and fixed with the silly button thingy too.
 
And how is a crimp or solder connection any less likely to be pulled apart whilst plastered in than a socket?

It's not just pulling apart. When cables are terminated within an enclosure e.g. the back box of an accessory, there should be some slack that allows for a bit of differential movement due to thermal cycling of the terminal and conductor. If the cable is rigidly plastered in directly up to the terminal, any thermal stresses are more likely to be transferred to contact surfaces and accelerate frettage corrosion.

There is indeed some BS in some of the products but the technology of terminals and connection methods is more complex than it looks and is not just manufacturers trying to fleece you. It's a field that I study because I need to make high-reliability connections. I don't like the MF specs as they are, but I can understand how and why they have evolved the way they have.

Re. crimps, many generic products are not made to any particular specs of any significance. They are just random bits of bent metal that work for Joe Bloggs to add a pair of aftermarket fog lamps to his car. Once you start digging through the detailed specs of the proper products from the likes of Klauke, AMP etc you start seeing the differences.
 

Reply to Jointing cable in wall to be filled and wiring zones in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
912
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
244
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
691
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock