DanielGemmell

sorry if this has been posted in the incorrect place.

was at a friends house and since wedensday he has been unable to turn off the kitchen light.
i checked the light and all the connections are fine.
at the switch I'm getting 230v between live and cpc and 230v between neutral and cpc

both light and switch only have 1 cable at it which suggests its a joint box between the ceiling and the floor of upstairs.

i have yet to look in the board but i genuinely do not know hat could be wrong.

FYI i am still an apprentice so forgive me
 
sorry if this has been posted in the incorrect place.

was at a friends house and since wedensday he has been unable to turn off the kitchen light.
i checked the light and all the connections are fine.
at the switch I'm getting 230v between live and cpc and 230v between neutral and cpc

both light and switch only have 1 cable at it which suggests its a joint box between the ceiling and the floor of upstairs.

i have yet to look in the board but i genuinely do not know hat could be wrong.

FYI i am still an apprentice so forgive me

You sure?
 
Busted switch I reckon, at the switch with only one cable, you will have a live and a switched live not a neutral, if you are getting 230v to earth at the live and switch live, operate the switch and see if the voltage disappears from the switched live, then as I said more than likely a busted switch.
 
Isolate the circuit using the MCB or CU main isolator, disconnect one wire from the switch and make it safe by putting it into a wago or choc block. Re-energise the circuit, if the light is off then replace the switch, if it's still on then start by running a full circuit test and interrogate your friend after slipping him some sodium pentothal because my money would then be on him having done some DIY replacing of the fitting :).
 

Reply to Kitchen Light will not switch off only started happening recently in the UK Electrical Forum area at ElectriciansForums.net

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock