32amp rfc supplying two gang sockets in wall behind kitchen units. At present horrible holes have been cut in the back of the units to get access to the sockets for appliances. New units going in. Whats the best way of extending to a pattress in the back of the unit? In essence Im looking for and unfused connection unit that will fit to a double back box.
 
@ Buzz,
or better still put a planking plate on and come out off the back box by extending the cable .
So what is the difference with my suggestion, which you disagreed with?? I would extend the cables using a maintenance free joint within the back box and cover over with a blanking plate.
[automerge]1568634441[/automerge]
Yes, could do but am somewhat surprised that there isn't a purpose built product especially as this must be quite a common scenario. Perhaps Im over complicating things!
I agree, which is why I suggested a maintenance free joint since the blanking plate may not be easily accessible.
 
Just trying to get a neat way of routing the cable through the blanking plate which ideally would need some sort of clamp to protect it from being pulled and stressing the actual conductor connectors.
 
if you put a maintenance free in side the back box does it defeat the job .it is no difference then then putting in wagos .
Sorry Buzz, but I really don't understand your point?
The back boxes are already there and make for a good enclosure, a "maintenance free" joint is more reliable than a screw connection but just as easy to install, the blanking plate forms an almost neat flush enclosure cover but remains accessible (though limited by the kitchen cupboards in this case) should the joint ever need exposing in a worst case scenario.
 
Sorry Buzz, but I really don't understand your point?
The back boxes are already there and make for a good enclosure, a "maintenance free" joint is more reliable than a screw connection but just as easy to install, the blanking plate forms an almost neat flush enclosure cover but remains accessible (though limited by the kitchen cupboards in this case) should the joint ever need exposing in a worst case scenario.

You don't get many maintainence free joint boxes that will fit inside a flush box though.
Wago's in the flush box are a sensible alternative to screw terminals, but this is not a maintainence free joint because the manufacturer has not specified it as such.
 
You don't get many maintainence free joint boxes that will fit inside a flush box though.
Wago's in the flush box are a sensible alternative to screw terminals, but this is not a maintainence free joint because the manufacturer has not specified it as such.
Right, so the crux of this conversation is what is actually defined as a "maintenance free" joint. I never specified what style of joint.
 
Right, so the crux of this conversation is what is actually defined as a "maintenance free" joint. I never specified what style of joint.
Exactly, Wago only state MF when using their connectors in their correct enclosure as an example.
 
wagos in a standard back box with blanking plate be fine. . maintenance free by definition or just plain common sense.
My point, the manufacturers are just covering their a***s in case of liability.

If you want to do it totally by the manufacturer's recommendations then chop out the back boxes make the holes bigger and fix back the wago's enclosure. (complete waste of time and effort in my opinion)
[automerge]1568636736[/automerge]
If this is going to turn into a debate on definitions then I retract my original suggestion of "maintenance free" and re-place it with "requires minimal maintenance". :rolleyes:
 
Thanks for the responses folks. Just makes you wonder how many non MF sockets and connection units are hidden and inaccessible behind fitted kitchen units :eek:

Thousands and possibly millions...

Rip out a kitchen that was fitted in the 1980s or 1990s and I would bet my bottom dollar you will find at least one totally hidden jointed cable
 
32amp rfc supplying two gang sockets in wall behind kitchen units. At present horrible holes have been cut in the back of the units to get access to the sockets for appliances. New units going in. Whats the best way of extending to a pattress in the back of the unit? In essence Im looking for and unfused connection unit that will fit to a double back box.
Might have to fit a double accessory box and fit fcu and a single socket
 
No. Just need to jump across the service gap at the rear of unit and feed a new surface mounted double socket.

Arrgh. I was going to suggest an access panel for maintenance purposes.

When I did kitchen refurbs and socket outlet point (now behind new floor unit) was required to be reused, I'd rewire it, priced accordingly. Its going to be a bit of a bodge (IMO), trying 'jump across the service gap'.
 
In my experience, you sometimes wonder how an expert joiner, who spends days fitting a kitchen, perfect mitre on the worktop, but cant cut a simple square hole to access a socket behind a unit. Last one I worked on, the joiners left a hole.... I cant say if its a square with curved sides or a circle with corners.

Same job. Microwave in wall unit with socket in unit above. I'd left the socket on a deep pattress... all the joiner had to do was cut a square hole so the socket would protrude through into the unit.... Nope.... 2 inches off measurement. I had to come back and move the socket to suit HIS hole.
 
In my experience, you sometimes wonder how an expert joiner, who spends days fitting a kitchen, perfect mitre on the worktop, but cant cut a simple square hole to access a socket behind a unit. Last one I worked on, the joiners left a hole.... I cant say if its a square with curved sides or a circle with corners.

Same job. Microwave in wall unit with socket in unit above. I'd left the socket on a deep pattress... all the joiner had to do was cut a square hole so the socket would protrude through into the unit.... Nope.... 2 inches off measurement. I had to come back and move the socket to suit HIS hole.
i'd have altered his hole ( and i don't mean the hole in the kitchen unit). once had similar. builder/joiner cut hole on board for a double socket, even after i told him that i'd do it. when i fitted the socket, it was 3 inches lower than the other one 4ft. away. customer wanted me to pay to reboard that section of wall. i said how does pi$$ off sound. get the builder back.
 
yeah. pointless fitting an enclosure within another enclosure.
 
I have seen a twin blanking plate drilled out and connector blocks used to make a ‘make shift’ connection plate
Funnily enough having purchased a couple of MK blanking plates, it can be seen that they incorporate two knock/drill out areas suitable to take a cable out.
CC8E9994-33F7-4D71-B127-007536B42404.jpeg
 
found this today so as was said before its amazing what you find in a kitchen
IMG_1232.JPG

[automerge]1568823836[/automerge]
The cooker cable was similar with 3 sets of joints in one pice of cable. Easy fix lift hatches pull cables under floor and re route but as was pointed out this isn't always possible
 
Funnily enough having purchased a couple of MK blanking plates, it can be seen that they incorporate two knock/drill out areas suitable to take a cable out.
View attachment 52313
Used these for similar purpose to the OP, just use wagos in the back box but double the cables over avd cable tie to give additional stress relief. If someone gives it a real tug they'll bring the whole lot through the blanking plate before the cable joint fails.

Show willing and apply some common sense.
 
found this today so as was said before its amazing what you find in a kitchenView attachment 52326
[automerge]1568823836[/automerge]
The cooker cable was similar with 3 sets of joints in one pice of cable. Easy fix lift hatches pull cables under floor and re route but as was pointed out this isn't always possible

If you do regular work in houses and flats you will come across these tape joints on a daily basis

What amazes me is that they remain buried under plaster or cement for decades without problem
 
Interesting discussion. I'm not saying I wouldn't do what you propose, but are we not breaking reg 526.3 doing it this way? I do agree that it seems pointless putting an enclosure inside another enclosure, so would this be considered a departure?
 
Interesting discussion. I'm not saying I wouldn't do what you propose, but are we not breaking reg 526.3 doing it this way? I do agree that it seems pointless putting an enclosure inside another enclosure, so would this be considered a departure?
Yes, but it is a highly sensible solution to the problem that will never give any cause for concern. It also looks a lot tidier than a wago box hanging out of an open back box.
 

Reply to Kitchen refit - sockets moved from wall to units? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
948
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
943
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
288
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
478

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top