Search the forum,

Discuss Kitchen Socket Circuits?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Thoughts please... probably heard it all before ;-)
At some point I will be having a new kitchen fitted and I am going to be carrying out all the electrical works and any advice on the modern wiring methods of today would be appreciated.
I'm used to the old wiring methods, where it was about switching appliances below on/off from above the worktops. Fast forward and its all about hiding stuff away with hardly anything on show. The kitchen fitters love it, my electrical friends love it who are actively installing new kitchens and so does the wife :)
Below is what I've been toying with in my thoughts.....

Option 1: Dedicated RFC for appliances on a grid switch setup mounted on the back of a wall unit switching un-switched s/s/o mounted behind the appliances from each named d/p grid switch. General sockets above worktop to keep on existing house RFC. Cooker Switch to be mounted next to grid setup. Fridge/Freezer possibly on its own dedicated circuit and combo/microwave on another dedicated within the grid setup. (Everything in one place)

Option 2: Dedicated kitchen RFC only with sockets for all appliances in adjacent cupboards with general sockets above the worktop on the same RFC. Every socket on the ring and no un-fused spurs. (Everything else the same as above regarding Fridge, micro/combo)

Option 3: Old School method.... in the past apparently.
 
Grid switching is good for some things but its ultimately down to you, its your kitchen so install what is most convenient and within your budget. Bear in mind that with your option 1 idea of having the fridge/freezer on a separate circuit , then i assume this would be a new one? in which case it then becomes notifiable as a new circuit where as if you keep everything running from an existing ring then it stays as minor works. whether you are competent enough to test and sign off your own minor certificate only you know?
 
Yes Gavin, I understand exactly what you are saying. I am competent but due to the fact I'm not Part P registered as I don't require this in my line of work.
I will be getting a third party to sign off my works as a new consumer unit will also be fitted. :)
 
Fast forward and its all about hiding stuff away with hardly anything on show. The kitchen fitters love it, my electrical friends love it who are actively installing new kitchens and so does the wife

I have this really old fashioned idea that electrical controls should be conveniently sited for what they serve

Socket outlets sited so that chords and arms don't become mangled using these items

Cooker switches not mounted behind the Weetabix should a fast isolation be needed

The number of outlets sufficient and sited so that appliances are not serving multiple loads and requiring the person to plug and unplug needlessly

I believe a Kitchen is a "Workstation" where preparation and the serving of food is the primary function:eek:

I suppose these old fashioned ideas may have given way to a room that presents a kindly appearance rather functionality:(
 
Decent size radial, say 32 amp fed in either 4 or 6mm depending on reference method to a grid switch for some appliances. Working on the principle you won't have the dishwasher, washing machine and tumble drier on at exactly the same time.

Rest of the sockets on an RFC or radials as required.

I see no real need for dedicated circuits for fridge/freezers etc in domestic, if they keep on tripping the RCD they normally need replacing anyway and it's a good indication when the kettle won't boil that something is wrong.

TBH all the sockets in my house are run off one RFC upstairs with cable drops to the ground floor and never had any issues. However the kitchen is being ripped out next year and I will be designing the kitchen power to be a little better than the existing 70's design.
 
Fast forward and its all about hiding stuff away with hardly anything on show. The kitchen fitters love it, my electrical friends love it who are actively installing new kitchens and so does the wife

I have this really old fashioned idea that electrical controls should be conveniently sited for what they serve

Socket outlets sited so that chords and arms don't become mangled using these items

Cooker switches not mounted behind the Weetabix should a fast isolation be needed

The number of outlets sufficient and sited so that appliances are not serving multiple loads and requiring the person to plug and unplug needlessly

I believe a Kitchen is a "Workstation" where preparation and the serving of food is the primary function:eek:

I suppose these old fashioned ideas may have given way to a room that presents a kindly appearance rather functionality:(
I know... peer pressure comes to mind!
Option 1 appears to be a widely used method on lots of new builds these days.
 
agree with des. a kitchen is there to prepare and cook food. end of. therefore all electrical works should reflect this and make the kitchen fit for purpose. any customer that does not want to see accessories on show should bin the oven and use mcdonalds/burger king/local pizza takeaway.
 
I'd go for option 2 , keep it nice and simple !
agree with des. a kitchen is there to prepare and cook food. end of. therefore all electrical works should reflect this and make the kitchen fit for purpose. any customer that does not want to see accessories on show should bin the oven and use mcdonalds/burger king/local pizza takeaway.
agree with des. a kitchen is there to prepare and cook food. end of. therefore all electrical works should reflect this and make the kitchen fit for purpose. any customer that does not want to see accessories on show should bin the oven and use mcdonalds/burger king/local pizza takeaway.
I take it yourself and Des56 like the accessories on show..... option 1 & 2 out of the question on your kitchen installs then?
Would your preferred preference be 6 way grid on show or 6 x d/p switches or switched fused spurs scattered around above worktop controlling appliances?
 
The are an awful lot more options than what you have listed.

Where is the fuseboard in this installation?
 
I take it yourself and Des56 like the accessories on show..... option 1 & 2 out of the question on your kitchen installs then?
Would your preferred preference be 6 way grid on show or 6 x d/p switches or switched fused spurs scattered around above worktop controlling appliances?

Paul I said 'Option 2' - normal use sockets above worktops and surface mounted appliance sockets in adjacent base units, so no clutter of switched fused spurs or expensive grid assemblies .
 
Fast forward and its all about hiding stuff away with hardly anything on show. The kitchen fitters love it, my electrical friends love it who are actively installing new kitchens and so does the wife

I have this really old fashioned idea that electrical controls should be conveniently sited for what they serve

Socket outlets sited so that chords and arms don't become mangled using these items

Cooker switches not mounted behind the Weetabix should a fast isolation be needed

The number of outlets sufficient and sited so that appliances are not serving multiple loads and requiring the person to plug and unplug needlessly

I believe a Kitchen is a "Workstation" where preparation and the serving of food is the primary function:eek:

I suppose these old fashioned ideas may have given way to a room that presents a kindly appearance rather functionality:(
The are an awful lot more options than what you have listed.

Where is the fuseboard in this installation?
The are an awful lot more options than what you have listed.

Where is the fuseboard in this installation?
Paul I said 'Option 2' - normal use sockets above worktops and surface mounted appliance sockets in adjacent base units, so no clutter of switched fused spurs or expensive grid assemblies .
Paul I said 'Option 2' - normal use sockets above worktops and surface mounted appliance sockets in adjacent base units, so no clutter of switched fused spurs or expensive grid assemblies .
Thanks Dave OCD... :)
 
Decent size radial, say 32 amp fed in either 4 or 6mm depending on reference method to a grid switch for some appliances. Working on the principle you won't have the dishwasher, washing machine and tumble drier on at exactly the same time.

Rest of the sockets on an RFC or radials as required.

I see no real need for dedicated circuits for fridge/freezers etc in domestic, if they keep on tripping the RCD they normally need replacing anyway and it's a good indication when the kettle won't boil that something is wrong.

TBH all the sockets in my house are run off one RFC upstairs with cable drops to the ground floor and never had any issues. However the kitchen is being ripped out next year and I will be designing the kitchen power to be a little better than the existing 70's design.

Might be a squeeze getting 6.0mm cables in a grid system
 
lost count of the number of burnt out grid switches i've seen. some just defunct, some bridged out due to failure. only ever fitted 1 4 gang grid for kitchen appliances. bit me in the arse when the freezer switch failed and customer hit me with a £300 bill for ruined food. never again on my watch.
 
What ever you decide just don't have the plugs for the appliances behind the appliances ....
Never a socket behind an integrated appliance, but a trailing socket on the other hand is fine. Gives a lot of flexibility in the installation as well.
 
lost count of the number of burnt out grid switches i've seen. some just defunct, some bridged out due to failure. only ever fitted 1 4 gang grid for kitchen appliances. bit me in the arse when the freezer switch failed and customer hit me with a £300 bill for ruined food. never again on my watch.
Thanks for the reply.... all the grid set ups seem to be the norm in new builds these days. Plenty of call outs then if that's a common occurrence then!
 
Never a socket behind an integrated appliance, but a trailing socket on the other hand is fine. Gives a lot of flexibility in the installation as well.
Not sure about that one... why without sounding rude?
I've heard of quick flow connectors on appliances that have had there plugs cut off? A bit like the flex outlet method of old which I never liked.
 
Not sure about that one... why without sounding rude?
I've heard of quick flow connectors on appliances that have had there plugs cut off? A bit like the flex outlet method of old which I never liked.
Just to add if there's a problem with an appliance... it has to come out regardless of where the plug in point is anyway.
 
Use grids all the time never had a problem with them Either 4 gang 3 or 2.
They are a particular favourite of most of the house builders and are specified on the drawings for the kitchen layout.
Not sure why it’s a problem putting a socket behind an appliance either as is the norm with new builds our company carry out and I’m unaware of any problems while doing this.
If the appliances are tight tho then the appliance fitter will advise and we fit an a unswitched fused spur with flex outlet but always behind the appliance which is controlled by a DP switch in a grid set up.
 
Use grids all the time never had a problem with them Either 4 gang 3 or 2.
They are a particular favourite of most of the house builders and are specified on the drawings for the kitchen layout.
Not sure why it’s a problem putting a socket behind an appliance either as is the norm with new builds our company carry out and I’m unaware of any problems while doing this.
If the appliances are tight tho then the appliance fitter will advise and we fit an a unswitched fused spur with flex outlet but always behind the appliance which is controlled by a DP switch in a grid set up.
Do you have the grid on show?
 
Against the ceiling in the downstairs toilet, a few metres from the kitchen.
Lets hear your preferred method?
A little far away

I have no preferred method, every kitchen is different.

From Pull Up Sockets in the worktop, to pull down sockets hidden in the wall units. Isolators in a Larder unit for appliances to some grid switching, or a sub DB for appliances. Also have the likes of a bank of switches contolling contactors, but that can get expensive.
 
lost count of the number of burnt out grid switches i've seen. some just defunct, some bridged out due to failure. only ever fitted 1 4 gang grid for kitchen appliances. bit me in the arse when the freezer switch failed and customer hit me with a £300 bill for ruined food. never again on my watch.
If it was a fault with the grid module and not an installation error then I'd be chasing the wholesaler about the bill for that...

Unless you bought it off ebay or the like, in which case good luck chasing that up
 
Not sure about that one... why without sounding rude?
I've heard of quick flow connectors on appliances that have had there plugs cut off? A bit like the flex outlet method of old which I never liked.
With Integrated appliances, Dishwasher especially but some makes of Fridge/Freezer and other appliances...there is no space for the plug & socket so the appliance can't be pushed back.
 
When it's the plug or socket that's faulty .......

Each to their own ....

The 18th should explicitly state how these connections should be achieved.
Why should it? I don't see a need for BS7671 to give a step by step guide of how every installation should be done.

Tumble Dryers aside I think I have yet to come across a plug that's gone faulty on a domestic appliance without another fault present.
 
I have lost count how many times a tripping rcd has been traced to an appliance with the plug in an inaccessible position
I have lost count how many times a tripping rcd has been traced to an appliance with the plug in an inaccessible position
Switch all grid switches off or all separate switches , reinstate rcd, switch on one by one, rcd trips on faulty appliance.... fault found. To be honest customers or non electrical people struggle to reinstate an rcd under fault conditions anyway regardless of the position of the sockets. The key bit is that these sockets are preferably double pole switched indirectly or unplugged directly to find a problem, with an understanding of very basic fault finding knowledge.
 
With Integrated appliances, Dishwasher especially but some makes of Fridge/Freezer and other appliances...there is no space for the plug & socket so the appliance can't be pushed back.
Okay.. I understand. I will be spacing my kitchen base/tower units out due to starting with a blank canvass.
 
until appliance manufacturers make allowances for a socket outlet & plug behind their stupid appliances, this debate will go on for years. it's not rocket science. appliance needs electricity to work. this is usually supplied by a socket outlet. that's why they fit plugs on their appliances. one day they might realise that these plugs what they fit are not just for decoration. they need to be plugged in to a suitable socket within reach of their ridiculously short leads.
 
A little far away

I have no preferred method, every kitchen is different.

From Pull Up Sockets in the worktop, to pull down sockets hidden in the wall units. Isolators in a Larder unit for appliances to some grid switching, or a sub DB for appliances. Also have the likes of a bank of switches contolling contactors, but that can get expensive.
Thanks for adding
 
until appliance manufacturers make allowances for a socket outlet & plug behind their stupid appliances, this debate will go on for years. it's not rocket science. appliance needs electricity to work. this is usually supplied by a socket outlet. that's why they fit plugs on their appliances. one day they might realise that these plugs what they fit are not just for decoration. they need to be plugged in to a suitable socket within reach of their ridiculously short leads.
What's your preferred method anyway?
 
The only person who would ever think that having an isolation switch in plain view as a preferred option is an electrician or geek. And don't get me onto grid switches. In the last 10 years in my kitchen I have never had to turn off an appliance quickly, and if I had, I could have isolated it by either using the plug in the cupboard next to the appliance or using the functional switch for the circuit in my consumer unit. All appliances are fed from switched single socket outlets in the adjacent cupboard and I always fit kitchens this way. Modern appliances are generally low power consumption so don't sweat the small stuff, put it all on a kitchen rfc, get those switches hidden away, forget about them and move on.:)
 
The only person who would ever think that having an isolation switch in plain view as a preferred option is an electrician or geek. And don't get me onto grid switches. In the last 10 years in my kitchen I have never had to turn off an appliance quickly, and if I had, I could have isolated it by either using the plug in the cupboard next to the appliance or using the functional switch for the circuit in my consumer unit. All appliances are fed from switched single socket outlets in the adjacent cupboard and I always fit kitchens this way. Modern appliances are generally low power consumption so don't sweat the small stuff, put it all on a kitchen rfc, get those switches hidden away, forget about them and move on.:)
Cooker switch... on show or hidden away like your skts in adjacent cupboards?? Like your passion and straight the point answer
 
The only person who would ever think that having an isolation switch in plain view as a preferred option is an electrician or geek. And don't get me onto grid switches. In the last 10 years in my kitchen I have never had to turn off an appliance quickly, and if I had, I could have isolated it by either using the plug in the cupboard next to the appliance or using the functional switch for the circuit in my consumer unit. All appliances are fed from switched single socket outlets in the adjacent cupboard and I always fit kitchens this way. Modern appliances are generally low power consumption so don't sweat the small stuff, put it all on a kitchen rfc, get those switches hidden away, forget about them and move on.:)
Cooker switch... on show or hidden away like your skts in adjacent cupboards?? Like your passion and straight the point answer
Cooker switch... on show or hidden away like your skts in adjacent cupboards?? Like your passion and straight the point answer
The only person who would ever think that having an isolation switch in plain view as a preferred option is an electrician or geek. And don't get me onto grid switches. In the last 10 years in my kitchen I have never had to turn off an appliance quickly, and if I had, I could have isolated it by either using the plug in the cupboard next to the appliance or using the functional switch for the circuit in my consumer unit. All appliances are fed from switched single socket outlets in the adjacent cupboard and I always fit kitchens this way. Modern appliances are generally low power consumption so don't sweat the small stuff, put it all on a kitchen rfc, get those switches hidden away, forget about them and move on.:)
If your not an electrician or a geek.... what are you then?
 
Cooker switch... on show or hidden away like your skts in adjacent cupboards?? Like your passion and straight the point answer

Hidden away of course, in a cupboard next to cooker, is a cooker switch a thing of beauty............no! The only time I need to find a cooker switch is when I change the cooker.
 

Reply to Kitchen Socket Circuits?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
793
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
943

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top