Hi gents

Just wondering if anyone can advise me on my working out.
Have been asked to advise on supply conductor csa for a sub distribution supply. The power requirements are 10kVA 400V supply.

I'm used to working with kW power just not sure on kVA - Amps formula which I have used below: -

I = 1000 x kVA / (1.732 x VL-L(V)
Therefore 10000 / (1.732 x 210V)
Therefore 10000 / 363.72
Amps = 27.49?

I'm a little confused as if I transpose kVA - KW :-
kVA x PF
10 x 0.95 = 9,500kW
So if I use 9.5kW,
9500 / 1.732 x 400 x PF (0.95)
my design current drops to 14.43Amps?

Any advice would be great thanks all
 
Your 1st calc was almost right, but where did you get 210V from?
Your 2nd calc was almost right as well, notice that the power factors cancel out, so you don't need it!
 
Your 1st calc was almost right, but where did you get 210V from?
Your 2nd calc was almost right as well, notice that the power factors cancel out, so you don't need it!

Cheers Archy, I took 210V to be Line voltage - line voltage.
I see what you mean about PF! Doh:)
Have I miscalculated tho somewhere as if I work out kW from kVA my result is different, substantially when I transfer kW to amps? It as if I haven't root3 correctly?
 
kVA is exactly what it looks like: kilovoltamps, so when you divide VA by the voltage, by definition you get the current. Hence it being called the apparent power, i.e. what the power appears to be from multiplying the voltage and current, without any regard to the power factor.

Real power in kW is the apparent power in kVA multiplied by the power factor, so if your power factor is less than unity the load won't be able to do as much useful work but the circuit current must still be calculated from the apparent power in kVA, without involving the power factor.

Note that for 3-phase power calcs the quick way in your head, it's not necessary to put sqrt(3) in anywhere. Just divide the rating in VA by the line-neutral voltage to give the sum of the line currents, then divide by 3 to get the line current. In your case (10k/230)/3 = 14.5A. It's useful to remember that a balanced 3-phase load on 400V takes 1.45A line current per kVA.
 

Reply to kVA - Amps Formula for Three Phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I have been tasked with seeing if a site is capable of accommodating a large new installation. I have done some working out but I'm not sure if...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock