14
hello.
I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021. However, once I bought it the nuisance tripping stopped, so I put it down to damp in garage at the time. This looks just like the Dilog6518 (just without dilog badge).
house is mid 1980s with wylex board 6 off mcbs with 30ma RCD protecting them all.

2 years later...
Grill has tripped rcd a couple of times in recent weeks (including last night). So I thought I'd use clamp meter to investigate, clamping meter over L-N meter tails dangling meter vertically.

results were:
10mA leakage initially
with kettle 48mA!
with kettle and grill 114mA!!

30mA RCD didn't trip in the test? It did trip when I pressed RCD test button.

q1
How accurate are these clamp meters? am I correct in letting meter dangle vertically from tails, as holding meter horizontally did seem to change reading significantly, also clamping main earthing conductor gave significantly lower reading.

q2
what is approximate, normal baseline leakage in house with no heating elements in circuit (e.g. fridge, CH, TV, broadband router, led lights etc.)?

q3
why didn't rcd trip during my test. even assuming meter readings weren't accurate 114mA does seem very high.

q4
any ideas how I can roughly assess meter accuracy? I guess warranty is expired now :)

I was going to replace board to Hagar with rcbo per circuit. I think I need to get to bottom of this issue first though.

thanks
 
I would guess the meter has a problem ,to assess its accuracy you could make a lighting circuit ( pendant on a plug with live and neutral wires separated from cpc)
insert a lamp and measure , it should read 0, set the meter to read maximum and hold and use (RCD) Residual Current Device tester or mft to set various currents, the clamp meter should read similar to the test current (within reason)
 

Reply to leakage clamp meter accuracy in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
7
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
4K
V.early days, just had installed solar. No battery, also supply of some parts difficult at the moment so no App or Online monitoring. I have a...
Replies
3
Views
3K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock