Hi, I’m Not getting enough torque on startup to turn pump. Turns pump successfully maybe 1 in 6 times on startup and then fine at full speed. Currently connected in star as per plate, 400V. Ran from a three phase inverter. Should this be wired delta? Still very much learning.
 

Attachments

  • 1421906E-BAD6-4D92-9024-DFC22980C099.jpeg
    354.1 KB · Views: 15
A VSD then. if it says 230V in and 400V out then the motor should be connected star.
This is a bit more of an 'upmarket' VSD than the ones I have used, but on the cheaper ones there's loads of parameters to set up.
 
Most single phase Input vsd have a 3 phase output of 230v between phases.
therefore a delta connection at the motor would be correct.
 
Hi, I’m Not getting enough torque on startup to turn pump. Turns pump successfully maybe 1 in 6 times on startup and then fine at full speed. Currently connected in star as per plate, 400V. Ran from a three phase inverter. Should this be wired delta? Still very much learning.
Is this inverter being fed from a 400v 3 phase supply?
if not then what is it being supplied with?
 

Reply to Learning electrical motors in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
797
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
652
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock