Search for tools and product advice,

Discuss LED bulbs flickering with time lag switch in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
I live in a condominium with a staircase lit by 9 LED bulbs of 10-11 w each. The bulbs are controlled by a time lag switch produced by Hager Electro, with 3-wire connection. Several months ago the lights started flickering, or even fading for several seconds and then going up again, in the timer mode of the switch. This did not happen, however, in the constant light mode. Putting the blame on the switch, I bought and installed a new one, of the same type but from a different manufacturer. To my extreme surprise, the phenomenon appeared again!
Then I went to measure the voltage on the input (L) and output (4) terminals of the switch relative to N. With the light switched off, the input was, as expected, the mains voltage of 223 v. With the bulbs lit and the switch in the permanent light mode, the voltage on both terminals was 208 v (voltage drop of 15 v probably due to internal resistance in the mains) and stable. However, in the timer mode the voltage fluctuated between 210 and 216 v. Thus we observe instability in voltage drop, which is due to instability in current, which in turn is due to instability in effective load resistance. Now the load consists of the same 9 bulbs plus the wires leading to them, so it must be constant. So where do the fluctuations come from?!
Another question: the observed voltage changes are small compared to the mains voltage, whereas the light changes are fairly strong. It is known that a LED works on DC voltage, which is obtained by rectifying the input AC voltage. Does this mean that there is some threshold voltage in the LED circuitry that cuts the input voltage at some some level close to 200 v, so that the above voltage fluctuations are felt very strongly?
Any reasonable explanation and advice should be appreciated.
 
I live in a condominium with a staircase lit by 9 LED bulbs of 10-11 w each. The bulbs are controlled by a time lag switch produced by Hager Electro, with 3-wire connection. Several months ago the lights started flickering, or even fading for several seconds and then going up again, in the timer mode of the switch. This did not happen, however, in the constant light mode. Putting the blame on the switch, I bought and installed a new one, of the same type but from a different manufacturer. To my extreme surprise, the phenomenon appeared again!
Then I went to measure the voltage on the input (L) and output (4) terminals of the switch relative to N. With the light switched off, the input was, as expected, the mains voltage of 223 v. With the bulbs lit and the switch in the permanent light mode, the voltage on both terminals was 208 v (voltage drop of 15 v probably due to internal resistance in the mains) and stable. However, in the timer mode the voltage fluctuated between 210 and 216 v. Thus we observe instability in voltage drop, which is due to instability in current, which in turn is due to instability in effective load resistance. Now the load consists of the same 9 bulbs plus the wires leading to them, so it must be constant. So where do the fluctuations come from?!
Another question: the observed voltage changes are small compared to the mains voltage, whereas the light changes are fairly strong. It is known that a LED works on DC voltage, which is obtained by rectifying the input AC voltage. Does this mean that there is some threshold voltage in the LED circuitry that cuts the input voltage at some some level close to 200 v, so that the above voltage fluctuations are felt very strongly?
Any reasonable explanation and advice should be appreciated.
I live in a condominium with a staircase lit by 9 LED bulbs of 10-11 w each. The bulbs are controlled by a time lag switch produced by Hager Electro, with 3-wire connection. Several months ago the lights started flickering, or even fading for several seconds and then going up again, in the timer mode of the switch. This did not happen, however, in the constant light mode. Putting the blame on the switch, I bought and installed a new one, of the same type but from a different manufacturer. To my extreme surprise, the phenomenon appeared again!
Then I went to measure the voltage on the input (L) and output (4) terminals of the switch relative to N. With the light switched off, the input was, as expected, the mains voltage of 223 v. With the bulbs lit and the switch in the permanent light mode, the voltage on both terminals was 208 v (voltage drop of 15 v probably due to internal resistance in the mains) and stable. However, in the timer mode the voltage fluctuated between 210 and 216 v. Thus we observe instability in voltage drop, which is due to instability in current, which in turn is due to instability in effective load resistance. Now the load consists of the same 9 bulbs plus the wires leading to them, so it must be constant. So where do the fluctuations come from?!
Another question: the observed voltage changes are small compared to the mains voltage, whereas the light changes are fairly strong. It is known that a LED works on DC voltage, which is obtained by rectifying the input AC voltage. Does this mean that there is some threshold voltage in the LED circuitry that cuts the input voltage at some some level close to 200 v, so that the above voltage fluctuations are felt very strongly?
Any reasonable explanation and advice should be appreciated.
could be the driver is either faulty or the wrong sort.
 
Perhaps your led lamps are not meeting the minimum load for proper operation? Have you checked the manufacturer literature?
I've just turned up this web page which suggests a solution, the customer has the same problem as you. Certain time delay switches are not suitable for led/low loads:

 
Last edited:
Try adding another load to the circuit,
try an incandesant lamp 100 to 150w.
See if it behaves better.
We had no problem of flickering or flashing with incandescent lamps. We replaced them with LEDs to save energy while gaining luminosity. I am almost sure that if we had an old-fashioned bi-metal time lag switch instead of electronic one, there would be no flickering. But they are not on sale any more.
 

Reply to LED bulbs flickering with time lag switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Good afternoon! I've recently wired a lighting system, where one light switch (a motion sensor) turns on two lights, but another motion sensor...
Replies
3
Views
1K
Hi, hopefully this is a quick one, in my new house I inherited a bathroom mirror with 4 small bulbs in it. This is hard wired to the main...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock