Discuss LED downlight flickering and going on and off intermittently in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all,

Have 6 x GU 5.3 LED downlights in the bathroom. Had no issues for 3 years and lights have started flickering and some go off for periods and come back on randomly. Changed the bulbs for new ones but exactly the same. There is no dimmer switch. Just a standard single way switch. HELP!!!
 
Are these LED lamps running on 12V electronic transformers that are designed for halogen lamps, with perhaps a minimum load of 20W?
 
Yes they are 12V 5W each but I don't know where the transformer is located (possibly in ceiling) to see what type and its power rating. Strange it's been fine for like 3 years though dont you think?
 
Typically there is one transformer per light, typically rated 20 to 60W. Though sometimes a larger transformer is used to power several lights. One reason to use smaller transformers per each light is they are then small enough to fit through the downlight holes, so if you drop the light fitting, it should be accessible (assuming whoever installed them left enough slack cable!). Of course, in an upstairs room the transformers can often be accessed from the loft.
 
Typically there is one transformer per light, typically rated 20 to 60W. Though sometimes a larger transformer is used to power several lights. One reason to use smaller transformers per each light is they are then small enough to fit through the downlight holes, so if you drop the light fitting, it should be accessible (assuming whoever installed them left enough slack cable!). Of course, in an upstairs room the transformers can often be accessed from the loft.
Great I will check if eXh has its own TX. My loft is converted and has laminate flooring so would like to avoid opening the floorboards
 

Reply to LED downlight flickering and going on and off intermittently in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Done a job yesterday, remove old 12v halogens and replace with mains, gu10 downlights. Fitted some LED gu10's no issues. Got a call today saying...
Replies
9
Views
885
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
237
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
742
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock