Discuss Led gu10 lights flashing on circuit in the Lighting Forum area at ElectriciansForums.net

Not sure about that one didnt have the other rooms on while trying dining room will do that on monday this is doing my head in niceic said i quote ( your circuit of led lamps are too big ) in total there are 23 on this circuit ive seen more then this and there worked fine with the same lamps but i will beat this one way lol
 
Easy to test the switch. Bypass the switch with a wire short and then power up the circuit.
Its possible the current draw of the lights is so low the awitch isnt engaging correctly.
But my guess is its more complex than that and its an interference being generated by the lamps.
You could try plugging them in while the circuits live. One light at a time. You may find you can get them all on ok. In which case its them all trying to start at the same time. The last light may need a resostive load to calm things down.
 
Easy to test the switch. Bypass the switch with a wire short and then power up the circuit.
Its possible the current draw of the lights is so low the awitch isnt engaging correctly.
But my guess is its more complex than that and its an interference being generated by the lamps.
You could try plugging them in while the circuits live. One light at a time. You may find you can get them all on ok. In which case its them all trying to start at the same time. The last light may need a resostive load to calm things down.
 
So it must be the electronics that drops the 230v to ELV in the lamp that is causing the supply to ripple. Its lije a mini startup surge. That is fed back down the supply feed and causes the other lights to switch off then back on and that just oscillates.
Look at this web page.

https://www.google.co.uk/url?sa=t&s...IYlH13gaEO0qk8PfQ&sig2=dKQviUC5eSqIVwC1GES-OA

Not quite the same but the solution looks right.
 
So it must be the electronics that drops the 230v to ELV in the lamp that is causing the supply to ripple. Its lije a mini startup surge. That is fed back down the supply feed and causes the other lights to switch off then back on and that just oscillates.
Look at this web page.

https://www.google.co.uk/url?sa=t&source=web&rct=j&url=http://forum.micasaverde.com/index.php?topic=9262.0&ved=0ahUKEwi4mt7sgIHQAhUJvRoKHTKHDzEQFggjMAA&usg=AFQjCNFZJNCcII-E_IYlH13gaEO0qk8PfQ&sig2=dKQviUC5eSqIVwC1GES-OA

Not quite the same but the solution looks right.
 
So it must be the electronics that drops the 230v to ELV in the lamp that is causing the supply to ripple. Its lije a mini startup surge. That is fed back down the supply feed and causes the other lights to switch off then back on and that just oscillates.
Look at this web page.

https://www.google.co.uk/url?sa=t&source=web&rct=j&url=http://forum.micasaverde.com/index.php?topic=9262.0&ved=0ahUKEwi4mt7sgIHQAhUJvRoKHTKHDzEQFggjMAA&usg=AFQjCNFZJNCcII-E_IYlH13gaEO0qk8PfQ&sig2=dKQviUC5eSqIVwC1GES-OA

Not quite the same but the solution looks right.
 
You have tried the lamps in another location and they are OK.
Therefore there is a problem with the wiring for the dining room light circuit.
Check and reterminate all the connections from when it leaves the previous room and change or by pass any switching and this should allow you to identify the problem.
It is possible that a continuity test from last point of supply to end of dining room lights may show a high resistance on line or neutral and allow you to identify the problem more quickly.
 
Between Richard's mine and others posts it could only be the wiring or lamps at fault but it would be nice if poster's came back and said what the problem(s) were found. It would be nice to know advice given had been helpful.
 

Reply to Led gu10 lights flashing on circuit in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Can I use multiple GU10 led lamps with their own PIR sensors in the same room? I have a row of existing lamps 600mm apart in a straight line & I...
Replies
9
Views
809
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
195
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
532

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock