- Reaction score
- 5,628
I have just fitted the manrose humidity/timer remote unit into a bathroom (see pic below)
When I switch the LED bathroom light off, it starts flashing. If I switch the TP switch for the extractor fan off it stops flashing. This only started happening when I introduced the humidity/timer remote unit.
I could understand if the LED light stayed on dimly, but why is it flashing? My idea was to fit a 230V snubber across L-N of the light, would this work? Is there a particular rated snubber that I need?
Could I just fit 2 x 160Kohm 1/4w (230V) resistors across L-N at the lamp?
Would these be suitable:
1. https://www.tlc-direct.co.uk/Produc...Vf7l0_PK95NUwqfCbCLK7uDq1xrzYX9EaArUHEALw_wcB
2. https://www.ebay.co.uk/itm/LED-Snub...ED-Bulbs-STOPS-Nausea-Migraines-/324163668142
3. https://cpc.farnell.com/ampohm-woun...-100/contact-suppressor-0-1uf-100r/dp/FT00715
Cheers
When I switch the LED bathroom light off, it starts flashing. If I switch the TP switch for the extractor fan off it stops flashing. This only started happening when I introduced the humidity/timer remote unit.
I could understand if the LED light stayed on dimly, but why is it flashing? My idea was to fit a 230V snubber across L-N of the light, would this work? Is there a particular rated snubber that I need?
Could I just fit 2 x 160Kohm 1/4w (230V) resistors across L-N at the lamp?
Would these be suitable:
1. https://www.tlc-direct.co.uk/Produc...Vf7l0_PK95NUwqfCbCLK7uDq1xrzYX9EaArUHEALw_wcB
2. https://www.ebay.co.uk/itm/LED-Snub...ED-Bulbs-STOPS-Nausea-Migraines-/324163668142
3. https://cpc.farnell.com/ampohm-woun...-100/contact-suppressor-0-1uf-100r/dp/FT00715
Cheers