Hi I wonder if you can help
In a rented property the kitchen has around 10 GU 10 halogen lights the tenant decided to replace these lights with new GU 10 lights And these days as you can only easily source LED GU10 Bulbs I’m almost certain the tenant has replaced the halogen lights with LED lights (I will go there and confirm this tomorrow).
The problem is now the RCD keeps tripping I went there before and had to replace the dimmer switch which had melted. I initially replaced it with another dimmer switch but I did not solve the problem and so I replaced it with a normal toggle switch. This has still not solved the problem the RCD continues to trip. From what the tenant tells me it’s only happens when the lights are first turned on if the breaker is reset then everything is fine.

to me this sounds like that there is a problem with the inrush current exceeding the RCD limits (the inrush current would also explain the burnt out dimmer switch)

what I would like to ask you all is what is the best solution I can

replace the LED bulbs with halogen bulbs Or does it make more sense to change the RCD from a type AC to a type A RCD and also change the MCB to a type C

Or am I barking up completely the wrong tree?

Many thanks in advance for any help or guidance you can provide.
 
check if the RCD is a RCBO. if so it could well be inrush current tripping the MCB part of the device. uprating to a C type may solve the problem.
 
Its usually the MCB that trips on in-rush current not the RCD.I would be testing insulation resistance first on the circuits feeding the RCD to see if any are down.The tenant could have trapped one of the cables when changing the lamps.I have never had 10 GU10 LED lamps cause an issue with in-rush before.
 

Reply to LED lighting replaced Halogen (GU10) in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi all, I am trying to replace my halogen wall uplights (230W, 240V, R7S, 114mm) with LED but so far no luck. I've tried both of the below LEDs...
Replies
5
Views
1K
I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
760
This is the second set which won't work to replace the current spots here in my kitchen. All they do is flash once quickly. I'm replacing...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock