If it's a TT installation then the 0.2/1 second disconnect times will apply for the final circuitsits, as you say agricultural by definition, and that does include processing facilities according to the definitions in the BYB.
the type S went out in 176ms but this is with it having 0.2 ze as it is at present, I cannot confirm how quickly it will operate if it is on TT.
The thing getting me in a tangle now is the discon times, in the agricultural section there is no mention of the 0.2/1sec times only the level of rcd protection, as post #16