I am working in a property that has the old steel painted switch back boxes that have no earth terminal. Came to light when testing R2 on the switch faceplate screws and got open circuit reading. Earth is present but just sleeved and folded over in the back box.

I intend to ring crimp the earth and clamp it under the fixing screws holding the back box into the brickwork, removing paint under the ring crimp to give good conductivity. Tested one and got a good R2 reading on the screws. Is this an acceptable method, obviously I don't want to start ripping boxes out the wall to install new galv back boxes.
 
or you could replace switches with metal facepates and use the earth terminal in the new faceplate. the 3.5mm pins would then give you an earth to the box.
 
I wouldn't put them under back box screws it isn't an earth terminal. Some back boxes have four lugs for front plate fixing and you could use one of them or drill and tap the back boxes but the brickwork gets through the drill bits. The previous Post to this is an excellent solution.
 
Or if they are plastic faceplates you could use nylon 3.5mm screws.
 
I can't to find a reg which would not permit what I am proposing. 134.1.4 seems ok and 526 i dont see anything there.
what about the fixing screw rusting over time and creating a high resistance contact. even if i say so myself. my post suggesting metal faceplates is a good solution and also improves the aesthetics. win win.
 
Most of the black painted switch boxes around here have plastic lugs so is not a problem, I take it yours have metal lugs though?

There is a reg which says a fixing screw can't double as an earth terminal, though I've no Idea which one. If the box gets knocked it could loosen the connection etc. Unlikely with a recessed box though. In the stores we have a load of MK earth terminals that would do the job, though the box would have to be removed from the wall to do it by which point it would be easier to replace the box!
 
what about the fixing screw rusting over time and creating a high resistance contact. even if i say so myself. my post suggesting metal faceplates is a good solution and also improves the aesthetics. win win.
Brass / Stainless Screw? I'm not knocking your idea though probably the best solution although costly.
 

Reply to Light Switch Back Boxes with no earth terminal in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
331
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
929
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
752
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
404
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock