I wonder if someone can tell me where I have gone wrong please.
I've changed my upstairs light switch from dimmer to normal switch.
I've Googled how to swap over the cables the light switch works when I'm upstairs but if I turn the light on from DOWN stairs I than can't turn it off from UPSTAIRS. It worked fine before when it was a dimmer.
I dont know how to paste the picture on here that I copied. Just wondered if it was something simple. Thank you
 
You;ve probably run into the issue of terminal labels not being consistent.

Some switches are COM, L1 and L2, others are L1, L2 and L3, so you can't always transplant L1 to L1.

A picture would definitely help, if not then a description of the colours in each terminal.

You may also need to check the wires at the bottom switch - as you need to match them at each end.
 

Reply to Light switch up stairs. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
848
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
597
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
626
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
682
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock